    Electrical Requirements for a 4 ton Acadia Air Handler

    This is mind boggling!
    I have a customer interested in installing the Acadia heatpump in his house and he is requesting the electriocal requirements for the Air Handler and 15k resistance heater. I told him 40 amps 220volt but when I called Hallowell to confirm this I was told that the requirements for the variable speed AH with the 15k resistance heater is 90 Amp!!!

    When I expressed my astonishment they told me their air handler is a York Generic variable speed.

    Can it possibly require 90amps?

  2. #2
    Join Date
    Jul 2008
    Posts
    54
    yes,if you used 10kw you would only need 60 amps

  3. #3
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    34,156
    I'd say any 15 kw air handler out there would require 90 amp single circuit or 60 & 30 for dual circuit.

  4. #4
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,058
    Yep.

    15 KW/240 volts = 62.5 amps
    62.5*1.25(continuous load duty circuit protection factor)=78.125amps circuit protection.
    Add on 3.5 amps for the 1 horse power VS motor. You need just over 80 amps total.
    So a 90 amp breaker.
    Or 1-30 amp, and 1-60 amp.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event