08-08-2008, 07:46 PM #1
Surprised No One Died...
Went to a clean and check in an older house in a golf course subdivision. The house was over 5,000 sq. ft. and had 3 Lennox G11 Conservator 80% furnaces from 1980-1981. They also had 3 A/C, 3 General humidifiers, and 3 Lennox EAC units.
All 3 furnaces had cracked heat exchanger panels. All panels. 2 had panels that looked like this:


The holes are baseball sized.
Oh, and I bet these A/C units work great!

The dude just bought the house and wants everything replaced now. WooHoo
lots of commissions for me.
-
08-08-2008, 11:16 PM #2
All 3 TXV bulbs were like this!?
I bet the compressor got flooded a few times.
-
08-09-2008, 12:59 AM #3
Regular Guest
- Join Date
- Sep 2002
- Location
- I don't know
- Posts
- 2,888
Out of curiousity how does the G11 get an 80% rating - do they have vent dampers?
-
08-09-2008, 01:42 AM #4
Professional Member*
- Join Date
- Jun 2008
- Location
- NW Florida
- Posts
- 701
I hope you shut the gas off to those units and tagged them even though it is probably to hot for heat.
As for the bulbs. Man I thought it was bad when the installers used tie wraps on the bulbs. That was not a hack job. Those guys where idiots.
-
08-09-2008, 08:15 AM #5
-
08-09-2008, 12:31 PM #6
Did the furnaces have rollout safeties them? Were they working or jumped out? As for the TXV bulbs, how many compressors did they go through? What a mess!!
Last edited by ldmth44; 08-09-2008 at 12:32 PM. Reason: question
Psalm 51:10, 12
-
08-09-2008, 01:52 PM #7
other than the TXV bulbs not being insulated, what is wrong with them?
We have put in a few M-coils, and we mount the bulbs on the suction line right outside the coil. We use the strap that comes with the bulb of course, and then wrap the whole thing in cork tape. They have all worked well.
-
08-09-2008, 02:19 PM #8
Regular Guest
- Join Date
- Sep 2002
- Location
- I don't know
- Posts
- 2,888
The TXV bulb looks like it's mounted on top of the suction line insulation.
-
08-09-2008, 02:24 PM #9
-
08-09-2008, 03:12 PM #10
Professional Member*
- Join Date
- Jun 2008
- Location
- NW Florida
- Posts
- 701
-
08-09-2008, 06:17 PM #11
On top of all said. Any one notice the bulb is upside down? It should be turned 180* the keep the more saturated refer in the bulb. Probably the only thing that kept the flood back throttled down.
-
08-11-2008, 07:00 PM #12
All TXV bulbs were upside down and over the top of the insulation. They guy just moved in a month ago or so so I can't presume as to how many compressors they went through. The ones on there now were a tad noisy.

You're right that a G11 isn't even close to 80% however for explanation purposes it's easier than saying "not high efficiency". It goes out a steel flue.
The rollouts were never activated for some reason. There was very little soot too. All the faults were at the very rear of the exchangers.
All units were shut down so that someone would have to make multiple steps to reactivate them. I only killed the heat side. I let the A/C keep churning away.