    Please help explain

    Hi there, I have come to this forum looking for help figuring out what to do about my AC unit, and to be sure that I have exhausted all options. I am disabled on a low income, and am freaking out. I was out of town and my neighbor walking my dog called to tell me my AC wasn't working and it was boiling in the house.

    Long story short, the AC company came and checked it out. They left me an invoice that said "unit is locked pulling 120 amps, tried new hardstart did not help, old hard start had come apart due to high amperage draw. Needs new compressor."

    This is a 7 year old Rheem unit, don't know the size but when it was new it was high efficiency.

    I have a couple of questions, the first being about what that even means as far as pulling those amps. And why I had a hard start put in not even a year ago that had come apart? At the time the tech said it was optional, but would extend the life of the unit considerably. Well it has been 11 months.

    Next, I want to be sure I shouldn't call an electrician first. Everything was fine, and 2 weeks ago my neighbor came and installed a digital thermostat since the old one wasn't digital and he said I would save money. Immediately, the AC stopped working. He came out the next day and said one of the wires, that went from the thermostat to the compressor, had popped out. He put it back in, but said the wire was very thin. He came out yesterday and checked to see if that was the problem but he said the wire was in there, but I wonder if it is a problem with the thin-ness of the wire, or could somehow be related to the thermostat? It seems like a strange coincidence that the compressor appears to have been blown out by high amps.

    He is not an electrician.

    I have a call in to the tech who came out here since yesterday, but so far I haven't heard anything.

    But let's just say hypothetically that that same wire broke behind the wall. Would the AC tech be able to tell that when he checked the compressor? Or would he just assume the compressor was broken since he tried everything and couldn't get it to start?

    Anyone know how much the range is for something like this, if I do need a new compressor, in the Atlanta area?

    Thanks for any help you can provide, I just don't know what to do. And it is 9 am and already 86 degrees in here.

  2. #2
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    The thermostat wire doesn't effect the amp draw of the compressor.

    It only controls a contactor.

    The locked rotor amp draw means the compressor is seized.
    It was probably showing troubles when the tech was there last year, and that is why he recomended the hard start kit. To try and get you longer life from the compressor.

    You might want to se if your local Community Action Program can help you.

    As far as cost, we don't talk about prices here. As it varies from one area to the next.
    And it is against the rules.

  3. #3
    Join Date
    Aug 2008
    Posts
    4
    Post Likes
    Thread Starter

    Thanks!

    Hi, thanks for the info. Sorry to break the rules, I am so stinkin hot I guess I didn't take the time to read them and should have!

    Glad to know that it's probably not related to the thermostat, just a coincidence I guess.

    Sure wish there was a possibility of doing something else as a band-aid until I can figure out how to pay for a compressor.

  4. #4
    Join Date
    Mar 2007
    Location
    AR
    Posts
    2,489
    Post Likes
    Quote Originally Posted by piglet66 View Post
    Hi, thanks for the info. Sorry to break the rules, I am so stinkin hot I guess I didn't take the time to read them and should have!

    Glad to know that it's probably not related to the thermostat, just a coincidence I guess.

    Sure wish there was a possibility of doing something else as a band-aid until I can figure out how to pay for a compressor.
    Whats the model and serial for the outside unit. Most the Rheem I install come with a 10 yr. comp. warranty.

  5. #5
    Join Date
    Aug 2008
    Posts
    4
    Post Likes
    Thread Starter

    Model

    Well on the unit it says it is a Rheem Classic 10 SEER "Scroll Inside." Don't know how many tons, but it is for approx 1800 sq. ft. Knowing this builder, it's probably the minimum adequate size for this house. It never gets freezing cold in here, it works very hard.

    The AC guy wrote this info down on the service ticket:

    Model RAKA-048JAZ
    Serial 5432 M4400 06954

    This house was bought new less than 8 years ago.

    Thanks!

  6. #6
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    4 tons for 1800 sq ft. Thats a lot for most that size house in most areas.

  7. #7
    Join Date
    Aug 2008
    Posts
    4
    Post Likes
    Thread Starter
    Well I am glad to hear it is the right size. I keep seeing info to lead me to believe it is a 10 year warranty, but for some reason the distributor is telling my AC people it is only 5 years.

  8. #8
    Join Date
    Dec 2002
    Location
    Houston,Texas
    Posts
    23,010
    Post Likes
    Quote Originally Posted by piglet66 View Post
    Model RAKA-048JAZ
    Serial 5432 M4400 06954

    This house was bought new less than 8 years ago.

    Thanks!
    The RAKA has a 5 year compressor warranty and that is a fact.
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards" ~ Vernon Law

    "It's what you learn after you know it all that counts." ~ John Wooden

    "When the teachers become unteachable we're all in trouble" ~ Mr. Bill

    "Remember "Pro" is only a name, it's not always a mindset determined to do everything correctly" ~ Mr. Bill




  9. #9
    Join Date
    Mar 2007
    Location
    AR
    Posts
    2,489
    Post Likes
    Yes, 5 yrs. Would be oversized even where I live and its a hot, humid, mofo here.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •