    2-10VDC = Chilled temp

    Hey guys I am looking for either a chart or formula for what 2-10vdc signal equals in Chilled water temp

  2. #2
    Join Date
    Feb 2006
    Location
    SouthEastern Virginia
    Posts
    1,077
    Post Likes
    For what controller? Trane, York, McQuay? It depends on the range of the sensor. Look in the IOM of the product you are looking at. They typically have a temperature/resistance chart to help. If you know the range of the sensor(10,000 ohms for example) and the coefficient(NTC or PTC) you can figure out the dc voltage for a given temperature. Plot it on a chart in Microsoft Excel if you know to use charts. Say the operating range of the sensor is -40 to 120 degrees F. The span is 120- -40 or 120+40 = 160.Now if the coefficient is positive than at -40 the dc voltage would be 2 volts. At 120 degrees the dc voltage would be 10vdc. At 40 degrees the dc voltage would be 6vdc. Smell what I'm steppin' in? If the resistance of the sensor goes above or below the range then the sensor will appear as failed to the controller. This would be a linear type sensor.
    It might get loud!

  3. #3
    Join Date
    May 2007
    Location
    Surrey BC
    Posts
    120
    Post Likes
    Thread Starter
    It's for a Trane CGAFC30 Chiller with UCPII controls

  4. #4
    Join Date
    Feb 2006
    Location
    SouthEastern Virginia
    Posts
    1,077
    Post Likes
    kwhit,

    See the IOM I have attached.

    The Duke
    It might get loud!

  5. #5
    Join Date
    May 2007
    Location
    Surrey BC
    Posts
    120
    Post Likes
    Thread Starter
    Thanks