Thread: Low suction, high superheat.
-
08-06-2008, 04:02 AM #1
Regular Guest
- Join Date
- Aug 2008
- Location
- Estonia,Tallinn
- Posts
- 16
Low suction, high superheat.
Hi guys,
My first post here. We got a cooling cabinet, for cooling dampening solution for a printing press. 2 Compressors- ManeuropMT64 (R22) tandem , it's got plate HE for condensing and a plate HE for evaporating. Head 213 (14bar) Suction 41(2.9bar) at 78°F ambient. Subcooling 8°C, superheat 20°C. TXV Danfoss Tex2. There's an oil separator installed but it's undersized as oil circulates.
Liquid line filter OK and no pressure drop across liquid line. Also there's a suction line filter installed (no pressure drop across it thought).
When i looked at the sight glass i could see the refrigerant running.
I was told that for a system on R22 the suction pressure should be 68psi.
-
08-06-2008, 04:57 AM #2
Professional Member
- Join Date
- May 2004
- Location
- new jersey
- Posts
- 338
68 psi=40 degree evap temp,thats mostly air conditioning/comfort cooling applications.
-
08-06-2008, 05:41 AM #3
Regular Guest
- Join Date
- Aug 2008
- Location
- Estonia,Tallinn
- Posts
- 16
We're cooling dampening solution to 10°C.
We have a cabinet like this one in the next room on 407c and it has 71psi suction 198 head. And it's doing the exact same thing cooling dampening solution to 10°C
-
08-06-2008, 06:24 AM #4
Gedday Dave. If the system is fully charged you should have a clear sight glass. The fact you can see the refrigerant running in the glass says to me the system is short. That'd explain the low SP and high SH.
oil separators only stop about 80% of the oil.
How did you arrive at your SH and SC figures? Just to clear it up for me, you say the suction temperature leaving your evaporator is 12C and your liquid line temp is 32C. is that correct?Mistakes are a part of being human. Appreciate your mistakes for what they are: precious life lessons that can only be learned the hard way. Unless it's a fatal mistake, which, at least, others can learn from. Al Franken, "Oh, the Things I Know", 2002
-
08-06-2008, 06:48 AM #5
Regular Guest
- Join Date
- Aug 2008
- Location
- Estonia,Tallinn
- Posts
- 16
Suction line temp is 14°C , Liquid line temp is 34°C. SH is 20°C right now & SC is 8°C . I tried adding more refrigerant and only the discharge pressure grew (241psi) while suction was still at 41psi.
8°C SC as far as i know means i have a sufficient amount of refrigerant in the system.
I just started servicing this place. I tried adjusting the superheat and 1 turn made it from 20°C to 3°C and the suction froze over immediately.
My thought were that the TXV is dead. I checked the orifice and nothing was clogging it.
-
08-06-2008, 08:16 AM #6
You shouldn't adjust a TEX2 more than a quarter of a turn at a time.
After that, let it settle for 10 to 20 minutes before checking again.
it sounds to me that it's OK and only needs setting.Mistakes are a part of being human. Appreciate your mistakes for what they are: precious life lessons that can only be learned the hard way. Unless it's a fatal mistake, which, at least, others can learn from. Al Franken, "Oh, the Things I Know", 2002
-
08-06-2008, 08:39 AM #7
Regular Guest
- Join Date
- Aug 2008
- Location
- Estonia,Tallinn
- Posts
- 16
-
08-06-2008, 08:54 AM #8
20 is high, 3 is lowish. at 41 PSI your SST is -8. 3K SH will give you a suction temp of -5. You'll have ice on the suction line.
If you can get 3K SH from the system it's working. It looks like your problem is with the load on the system.
I'd suggest you've got a low flow through the evap heat exchanger or it's fowled.Mistakes are a part of being human. Appreciate your mistakes for what they are: precious life lessons that can only be learned the hard way. Unless it's a fatal mistake, which, at least, others can learn from. Al Franken, "Oh, the Things I Know", 2002
-
08-06-2008, 10:38 AM #9
Regular Guest
- Join Date
- Aug 2008
- Location
- Estonia,Tallinn
- Posts
- 16
I decided to take a look at the pump pressure and you were right, on the cabinet with the 407c ( 71psi suction) the dampening solution pump reads over 1.5 bars(21psi) , on this cabinet it reads lower than 0.5bar (7.1psi). Both cabinets have the same specs and pumps. Could this be the problem ?
-
08-06-2008, 11:18 PM #10Mistakes are a part of being human. Appreciate your mistakes for what they are: precious life lessons that can only be learned the hard way. Unless it's a fatal mistake, which, at least, others can learn from. Al Franken, "Oh, the Things I Know", 2002
-
08-06-2008, 11:58 PM #11
Regular Guest
- Join Date
- Aug 2008
- Location
- Estonia,Tallinn
- Posts
- 16
Yes, it was clogged with some fibers, i replaced it. I didn't increase the pressure that much, so i checked the pump turns out it's half dead. Overheating, low rpm's, which is not unusual because i was told that this pump was an original that came with the cabinet when they bought it 11 years ago.
I have put an order for a new pump, we'll see than. Should be here within a week.
-
08-07-2008, 06:05 AM #12Mistakes are a part of being human. Appreciate your mistakes for what they are: precious life lessons that can only be learned the hard way. Unless it's a fatal mistake, which, at least, others can learn from. Al Franken, "Oh, the Things I Know", 2002
-
08-11-2008, 06:23 AM #13
Regular Guest
- Join Date
- Aug 2008
- Location
- Estonia,Tallinn
- Posts
- 16
New pump arrived today, the flow was back to normal, but it hardly had any effect on the suction pressure. It's 45Psi now virtually no difference.
Can the problem be in the TXV ?