Air Handler Transformer
How can I tell if the transformer should be connected using the 208 option or the 240 option?
THe last transformer was connected using 240 by a service tech. However, it lasted about 8 days, and died last Saturday night. Got a freid to pick up a transformer from an HVAC supply. Paid a "professional " firm for the last one.
The air handler and the condenser unit both indicate 208/230. I don't know how the original transformer was connected, as I trusted the service company to connect properly. Now, after two blown transformers in the last 2 weeks, not sure they are connecting them correctly. The low voltage looks good from what I can tell, I just want to ensure that the high voltage is using the right lead.
Thanks for any suggestions. I need to know how to find out the correct option. THe condenser is an 11 year old Armstrong. Air handler is same age. Definitely worn, but they were still working. I am selling in a week, so don't want to have to replace for someone else.Last edited by s7220700; 08-05-2008 at 10:08 AM.
-
08-05-2008, 09:31 AM #2
Professional Member*
- Join Date
- Jul 2008
- Location
- Alabama
- Posts
- 658
-
08-05-2008, 09:43 AM #3
-
08-05-2008, 09:33 AM #4
Professional Member
- Join Date
- Mar 2005
- Location
- Houston, Texas
- Posts
- 11,646
Suggestion #1, remove pricing from your post.
-
08-05-2008, 09:47 AM #5
Call that company back.
They didn't find the problem. They only fixed the symptom.
Since its blowing the transformer. The new transformer would most likely be covered under their warranty.
Then they can check for the cause.
If you just put a new transformer in. It will only go out again.
Then the new home owners may back charge you. And you could end up with a much higher bill yet.
Please edit out the pricing, its not allowed here. Thank you.
As this is not a DIY site. You won't get any DIY instructions.
-
08-05-2008, 10:06 AM #6
New Guest
- Join Date
- Aug 2008
- Posts
- 2
Thanks
Hey guys. Thank you for the information. I will edit out the prices. I apologize. First post and was in a hurry. DIdn't read all the rules.
I agree with low voltage short. I am waiting for someone to arrive to help me ohm out wires. Visual inspection of the condensing unit didn't reveal any obvious wire rubs or burned components.
I found the answer to the 240 question as well. Didn't realize you couldn't answer questions like that. I will read some more posts when I have the time to get an idea of what is normally discussed.