Results 14 to 17 of 17
    Chandler AZ
    Compressor Problem
    Just got back from site ,it was close to mmy house. Found half of the evaporator return bends and the suction line was froste up .Should I check restriction on distributor or just change the coil . Coil s rusted badly .It's about 10 years old. Since lt's a rental house ,changing the air handler is out of the question .
    Yes you should checked for a resriction at metering device.
    Chandler AZ
    Like to thank the members for their advices . Finally figure out the problem . Disconnect return duct from air handler ,found a thick layer of dirt inside the evp. coil .Clean it up ,start unit back up , pressures are good and indoor temp. drop eight degrees within an hour .
    Jun 2005
    SW Wisconsin
    Proper trouble-shooting sequence!
    Quote Originally Posted by crazy eye View Post
    Like to thank the members for their advices . Finally figure out the problem . Disconnect return duct from air handler, found a thick layer of dirt inside the evap coil. Clean it up, start unit back up, pressures are good and indoor temp. drop eight degrees within an hour .
    That is why you should always follow a proper trouble-shooting sequence.
    With those symptoms, it is either an airflow evap heatload problem or, it is a refrigerant system problem. Always eliminate the airflow evap heatload situation, first. A proper system charge can never be achieved with an improperly heat-loaded evap coil.
    The blower wheel should have been checked, lint-filled blades, check underside of evap coil, clean coil, problem solved. - udarrell
    AOP Forum Rules: