    Compressor Problem

    Just got back from site ,it was close to mmy house. Found half of the evaporator return bends and the suction line was froste up .Should I check restriction on distributor or just change the coil . Coil s rusted badly .It's about 10 years old. Since lt's a rental house ,changing the air handler is out of the question .

  2. #15
    Join Date
    Jan 2004
    Location
    PA
    Posts
    70,428
    Post Likes
    Yes you should checked for a resriction at metering device.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  3. #16
    Join Date
    Dec 2007
    Location
    Chandler AZ
    Posts
    175
    Post Likes
    Like to thank the members for their advices . Finally figure out the problem . Disconnect return duct from air handler ,found a thick layer of dirt inside the evp. coil .Clean it up ,start unit back up , pressures are good and indoor temp. drop eight degrees within an hour .

  4. #17
    Join Date
    Jun 2005
    Location
    SW Wisconsin
    Posts
    5,684
    Post Likes

    Proper trouble-shooting sequence!

    Quote Originally Posted by crazy eye View Post
    Like to thank the members for their advices . Finally figure out the problem . Disconnect return duct from air handler, found a thick layer of dirt inside the evap coil. Clean it up, start unit back up, pressures are good and indoor temp. drop eight degrees within an hour .
    That is why you should always follow a proper trouble-shooting sequence.

    With those symptoms, it is either an airflow evap heatload problem or, it is a refrigerant system problem. Always eliminate the airflow evap heatload situation, first. A proper system charge can never be achieved with an improperly heat-loaded evap coil.

    The blower wheel should have been checked, lint-filled blades, check underside of evap coil, clean coil, problem solved. - udarrell