Results 1 to 13 of 17
    Chandler AZ
    Compressor Problem
    Just replaced a compressor on a Carrier condensing unit , m# 38YC060-301 s#3698E01142 , compressor m# SBD600C01 ,vacuum and weigh in charge R22 ,start up unit ,low side 75psi ,high side 290psi ,aftr unit ran for about five minutes ,low side drop to 55psi ,high side stay the same ,suction line and accumanator start frost up .Outdoor temp. 100 degrees, indoor temp.89 degrees. Draw 23 amp, name plate 30 amp.20 degrees subcooling . Front seat high side valve ,high side drp to zero ,low side only pull down to 25 psi and then went back ip to 55psi ,high side went up to 150 psi .Could it be the compressor not pumping 100% that cause the frost up ?
    Denver, CO
    Quote Originally Posted by crazy eye View Post
    compressor is fine you have a restriction in the system. Did you replace the filter dryer? Or install a new one if one was not installed?
    Now your seeing what took out the old compressor.
    Chandler AZ
    Compressor Problem
    Did replace the dryer .f the compressor is good ,should t be able to pull down to vacuum ?
    Western NC
    Yeah and whats gonna take out the new one too if its not located
    Western NC
    all depends on the system, total charge, any pressure switches, etc.etc...
    Denver, CO
    Also if it's a newer scroll compressor their is an internal relief that won't always alow you to pull the system into a total vaccume.
    Chandler AZ
    compressor Problem
    Condensing unit only have high pressure cut out . Three days ago replaced the thermostat . Old thermostat not energize the reversing valve ,unit was running on heat and compressor cut out . Two days later compressor triping breaker .When apply power to unit .loud banging noise and spark from compressor terminals .Compressor omh out ok and it's not grounded . Change compressor now I have this problem .
    Chandler AZ
    compressor Problem
    It is a Danfoss scroll omprssor .
    Denver, CO
    Thats why you can't pull a vaccume your probably doing this on a hot day and your high pressure cut out is opening the contacor.
    Chandler AZ
    comprssor Problem
    High side cut out did not open the contactor .Unit still running while low side pull down to 25psi . Did not do a acid test . Did check out the oil in the old compressor ,it's looks pretty clean . Can you tell a burnout from the oil .Or acid test is the only way to find out ?
    You can tell some acid burn outs from the oil with out the test kit.
    But that is not your current problem.
    talk to your service manager.
    Sounds like Run and start were shorted together, or comp. was locked, find the restriction, and stop blaming the compressor.