  1. #1
    Join Date
    Dec 2007
    Location
    Chandler AZ
    Posts
    168

    Compressor Problem

    Just replaced a compressor on a Carrier condensing unit , m# 38YC060-301 s#3698E01142 , compressor m# SBD600C01 ,vacuum and weigh in charge R22 ,start up unit ,low side 75psi ,high side 290psi ,aftr unit ran for about five minutes ,low side drop to 55psi ,high side stay the same ,suction line and accumanator start frost up .Outdoor temp. 100 degrees, indoor temp.89 degrees. Draw 23 amp, name plate 30 amp.20 degrees subcooling . Front seat high side valve ,high side drp to zero ,low side only pull down to 25 psi and then went back ip to 55psi ,high side went up to 150 psi .Could it be the compressor not pumping 100% that cause the frost up ?

  2. #2
    Join Date
    Jul 2008
    Location
    Denver, CO
    Posts
    4,229
    Quote Originally Posted by crazy eye View Post
    Just replaced a compressor on a Carrier condensing unit , m# 38YC060-301 s#3698E01142 , compressor m# SBD600C01 ,vacuum and weigh in charge R22 ,start up unit ,low side 75psi ,high side 290psi ,aftr unit ran for about five minutes ,low side drop to 55psi ,high side stay the same ,suction line and accumanator start frost up .Outdoor temp. 100 degrees, indoor temp.89 degrees. Draw 23 amp, name plate 30 amp.20 degrees subcooling . Front seat high side valve ,high side drp to zero ,low side only pull down to 25 psi and then went back ip to 55psi ,high side went up to 150 psi .Could it be the compressor not pumping 100% that cause the frost up ?
    compressor is fine you have a restriction in the system. Did you replace the filter dryer? Or install a new one if one was not installed?

  3. #3
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,727
    Now your seeing what took out the old compressor.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  4. #4
    Join Date
    Dec 2007
    Location
    Chandler AZ
    Posts
    168

    Compressor Problem

    Did replace the dryer .f the compressor is good ,should t be able to pull down to vacuum ?

  5. #5
    Join Date
    Feb 2008
    Location
    Western NC
    Posts
    2,504
    Quote Originally Posted by beenthere View Post
    Now your seeing what took out the old compressor.
    Yeah and whats gonna take out the new one too if its not located
    I fully support the military and the War on Terrorism.


    If you don't know, then don't do. If you don't know and still do, then be prepared to pay someone else a lot to undo what you did and then do it right.

    If you do know, then do. But do it right. Otherwise, you may not be doing it long.

  6. #6
    Join Date
    Feb 2008
    Location
    Western NC
    Posts
    2,504
    Quote Originally Posted by crazy eye View Post
    Did replace the dryer .f the compressor is good ,should t be able to pull down to vacuum ?
    all depends on the system, total charge, any pressure switches, etc.etc...
    I fully support the military and the War on Terrorism.


    If you don't know, then don't do. If you don't know and still do, then be prepared to pay someone else a lot to undo what you did and then do it right.

    If you do know, then do. But do it right. Otherwise, you may not be doing it long.

  7. #7
    Join Date
    Jul 2008
    Location
    Denver, CO
    Posts
    4,229
    Quote Originally Posted by crazy eye View Post
    Did replace the dryer .f the compressor is good ,should t be able to pull down to vacuum ?
    Also if it's a newer scroll compressor their is an internal relief that won't always alow you to pull the system into a total vaccume.

  8. #8
    Join Date
    Dec 2007
    Location
    Chandler AZ
    Posts
    168

    compressor Problem

    Condensing unit only have high pressure cut out . Three days ago replaced the thermostat . Old thermostat not energize the reversing valve ,unit was running on heat and compressor cut out . Two days later compressor triping breaker .When apply power to unit .loud banging noise and spark from compressor terminals .Compressor omh out ok and it's not grounded . Change compressor now I have this problem .

  9. #9
    Join Date
    Dec 2007
    Location
    Chandler AZ
    Posts
    168

    compressor Problem

    It is a Danfoss scroll omprssor .

  10. #10
    Join Date
    Jul 2008
    Location
    Denver, CO
    Posts
    4,229
    Quote Originally Posted by crazy eye View Post
    Condensing unit only have high pressure cut out . Three days ago replaced the thermostat . Old thermostat not energize the reversing valve ,unit was running on heat and compressor cut out . Two days later compressor triping breaker .When apply power to unit .loud banging noise and spark from compressor terminals .Compressor omh out ok and it's not grounded . Change compressor now I have this problem .
    Thats why you can't pull a vaccume your probably doing this on a hot day and your high pressure cut out is opening the contacor.

  11. #11
    Join Date
    Dec 2007
    Location
    Chandler AZ
    Posts
    168

    comprssor Problem

    High side cut out did not open the contactor .Unit still running while low side pull down to 25psi . Did not do a acid test . Did check out the oil in the old compressor ,it's looks pretty clean . Can you tell a burnout from the oil .Or acid test is the only way to find out ?

  12. #12
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,727
    You can tell some acid burn outs from the oil with out the test kit.

    But that is not your current problem.

    talk to your service manager.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  13. #13
    Join Date
    Apr 2007
    Posts
    623
    Quote Originally Posted by crazy eye View Post
    Condensing unit only have high pressure cut out . Three days ago replaced the thermostat . Old thermostat not energize the reversing valve ,unit was running on heat and compressor cut out . Two days later compressor triping breaker .When apply power to unit .loud banging noise and spark from compressor terminals .Compressor omh out ok and it's not grounded . Change compressor now I have this problem .
    Sounds like Run and start were shorted together, or comp. was locked, find the restriction, and stop blaming the compressor.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event