    I am pretty sure that we have decided on a contractor, just wanted to get some opinions on the systems we have narrowed it down to.
    We are now sure whether we should put the extra $$$ up front for dual fuel or stay with gas/AC (this is for our downstairs, we have a heatpump upstairs total house sq ft: 2250; downstairs 1100ish). Local rates are $.0894/kwh (+$7.01/month customer charge) and $1.437/therm (+$5.00/month customer charge).
    The systems we are looking at are:
    Heil VS90 Gas Furnace 75,000btu
    Heil DX1400 AC 2 ton
    or
    Heil DX1400 Heatpump 2 ton
    Oh, we live in Charlotte, NC.
    Also, do you have any rec's for a whole house media filter? We have also considered the 4" MERV 10 filter that sits where a 'normal' filter does. Any opinion on the UV light set-ups?
    Thanks!
    Anybody??? Please...
    Dual fuel will save you money on your heating bill. With your posted rates, the HP should be cheaper down to about 30 or 25°F outdoor temp.
    You may like this contractor, but does he like you?
    A 75,000 BTU 90% efficient furnace for 1100 sq ft first floor? Sounds too big. Unless you regularly get winter temps of -20°F. Or have walls of glass.
    Alabama
    HEil does make a 50 kbtu VS 90 furnace.
    That will be plenty of heat!!
    Hmm, good question! It will be replacing a 90,000btu furnace. I did ask him when he said 75k if that was still too big, but he didn't seem to think so with it being downstairs. I will question him further for sure! Any thoughts on a whole house filter? Thank you so much!
    1100 sq ft with living area above it in a mild climate? Even 50K is likely too big but about the smallest you can get in a 90.
    DC Metro Area (MD)
    A whole-house media air filter is good to have for better filtration and protection of the equipment.
    A media air filter is a good filer for any unit. As long as the duct can handle it.
    Remind your contractor that your have a conditioned space above your lower floor.
    Apr 2001
    Camel City, NC
    Heil
    I'm in W-S 1500sqft up & 650 dn. (family room). built in 1962. no insulation in walls. 75K input 80% heil gas, 60K output. Unless that is a 2 stage furnace I'm with others, to big. Yes I use a HP and switch to the furnace around 40Ί. Have been pleased with the savings.
    Be safe not fast. body parts don't grow back
    You guys are great!
    The model that we have chosen is a 2-stage w/ variable speed.
    As far as a filter, what brand/model have you found to be most effective? As far as the ductwork, it is 6" rigid metal...not sure other than that.
    Better get the right size furnace though.
    Do fall for the" it will recover quicker " BS.
    Honeywell, and Trion are the 2 I use.
    Sounds like I will have a busy day tomorrow... Either the guy I like will come to his senses on the btu's or I will be on the hunt for another one. There's no sense in replacing an old oversized furnace with a new oversized furnace. I'll be sure to report back. Thanks, again!
    Apr 2001
    Camel City, NC
    If the furnace is oversized and you have a central humidifier it won't run long enough = low humidity
    Same here but sometimes Aprilaire (spaceguard) in place of trion.