    size help on my updated manual j calculations
    HOME BUILT IN 1980
    ORIGINAL CENTRAL A/C WITH ELECTRIC HEAT 3 TON
    CAN YOU TELL ME IF THIS LOOKS RIGHT, I HAVE DOUBLE CHECKED ALL MY INFO FOR CALCULATIONS. LOOKS LIKE ORIGINAL WAS OVERSIZED AND I ACTUALLY ADDED ABOUT 350 SQ FT TO THE ORIGINAL CONTRUCTION WHEN I ENCLOSED CARPORT
    WHAT SIZE HEAT PUMP SHOULD I GO WITH? AND WILL 10KW HEAT STRIP DO?
    VARIABLE SPEED AIR HANDLER? ANY SUGGESTIONS WOULD BE HELPFULL.
    THANKS
    JAMES
    1642 SQ FT.
    ACH: SUMMER:.43 WINTER: .85
    ROUND DUCTS INSULATED IN ATTIC R2
    6" INSULATION IN ATTIC, 3 1/2 INSULATION IN WALLS
    Design Conditions: Baton Rouge, Louisiana
    Indoor: Outdoor:
    Summer temperature:74 Summer temperature:93
    Winter temperature:72 Winter temperature:29
    Relative humidity: 50 Summer grains of moisture: 116
    Daily temperature range: Medium
    Sensible Latent Total Total
    Gain Gain Heat Gain HeatLoss
    (BTUH) (BTUH) (BTUH) (BTUH)
    17,690 5,527 23,217 32,931
    Will It Matter If I Lower The Inside Temp To 72
    Quote Originally Posted by toireht View Post
    Yes ,lower indoor will increase btus required.
    Plus ,eqipment is rated at 80°F,with a reduction of the equipment's capability to produce sensible btus,of 835 btus X each degree below 80°,per every 1000 cfms.
    Check footnotes on mfrs literature ,for this info..