Is it OK to keep the existing evap. coil for R-410A with the new condensing unit?
My home has a split A/C system. The condensing unit is outside and the furnace and evap coil is inside the house. The evap coil was replaced on March 2008 with Trane model # 2TXCC049BC3HCAA. I need to replace the condensing unit with a new Trane unit model # 4TRR3048A100A that uses R-410A refrigerant. My existing system uses R-22. My question is: Is it OK to keep the existing evap. coil for R-410A with the new condensing unit? The A/C tech said if adding Thermal Expansion Valve (TXV) to the indoor coil and a suction drier , evacuate the current refrigerant ,clean both coil , the exiting evap.coil will work with r-410A.
The other A/C tech told me I need replace existing Evap.coil to matched with condenser. Who is right?
very much appreciate your opinions:
-
07-30-2008, 03:47 PM #2
Professional Member*
- Join Date
- Aug 2007
- Location
- Northern VA 38 degrees N by 76 degrees W
- Posts
- 3,251
-
07-30-2008, 03:53 PM #3
And did he tell you he would come back to remove the suction filter drier after a couple days.
You could just get an R22 condenser.
-
07-30-2008, 05:41 PM #4
If I had the new 2TXC coil, I'd just do what been said, get the R22 outdoor unit.
-
07-30-2008, 06:44 PM #5
Banned
- Join Date
- Aug 2002
- Location
- Office and warehouse in both Crystal River & New Port Richey ,FL
- Posts
- 18,836
We have done several conversions,22 to 410 coil,no issues.In our area it's heat pump air handlers ,sometimes VS,not just the coil.
-
07-30-2008, 06:59 PM #6
Banned
- Join Date
- Aug 2002
- Location
- Office and warehouse in both Crystal River & New Port Richey ,FL
- Posts
- 18,836
We have done several conversions,22 to 410 coil,no issues.In our area it's heat pump air handlers ,sometimes VS,not just the coil.
-
07-30-2008, 07:33 PM #7
Regular Guest
- Join Date
- Jul 2008
- Location
- North Dallas
- Posts
- 18
As long as all the oil can be removed from lines. Alkylbenzene doesn't mix to well with POE. Triple evacuation and very dry (low microns) required.
-
07-30-2008, 08:53 PM #8
Professional Member*
- Join Date
- Jul 2006
- Location
- Virginia
- Posts
- 3,714
iwould also ask for the r22 condensor and also you might still be able to get the 10 year parts and labor on the coil
-
08-04-2008, 11:54 AM #9
Regular Guest
- Join Date
- Jul 2008
- Posts
- 6
Thank you all for your help, We installed r-22 outdoor unit.
-
08-04-2008, 12:00 PM #10
Professional Member
- Join Date
- Aug 2003
- Posts
- 466