    Compressor Rated Amps

    I was checking a compressor that I could tell was not the factory installed one. It was a single phase, 44,000 Bristol. The label on the compressor only gave the lock rotor amps of 102. Is there some formula or trick to know what the running(RLA) amps are rated?

  2. #2
    Join Date
    Jan 2008
    Location
    Phoenix Arizona
    Posts
    1,663
    Post Likes
    "If history repeats itself I am so getting a dinosaur"

  3. #3
    Join Date
    Feb 2002
    Location
    Yuma, Arizona
    Posts
    952
    Post Likes
    Many text books say take the LRA and divide by 5 for RLA (and then use 80%).
    I tell my students to divide by 6. You get the same results more or less.

    Yuma,
    What is snow? Is it that white stuff in a freezer?

  4. #4
    Join Date
    Dec 2005
    Posts
    7,904
    Post Likes
    Thread Starter
    Quote Originally Posted by Yuma View Post
    Many text books say take the LRA and divide by 5 for RLA (and then use 80%).
    I tell my students to divide by 6. You get the same results more or less.

    Yuma,
    The LRA on my compressor was 102, and I read 15.5

    102 divided by 6 is 17. So its pretty close. I will remember it. Thanks.

  5. #5
    Join Date
    Aug 2001
    Location
    Mechanicsville, Virginia
    Posts
    2,042
    Post Likes
    An important note about FLA, RLA and LRA as they pertain to PSC (Permanent Start Capacitor) Compressors and PSC Fan motors.

    Compressor RLA (Rated Load Amperage) and Fan Motor FLA (Full Load Amperage) are located on the condenser or heatpump nameplate.

    Compressor RLA is the current drawn at the highest load conditions for which the compressor is rated to operate. Typically 115°F outside 80°/67° inside.

    The compressors internal overload will typically open at 1.5 times the Compressors RLA during continuous operation (or if the maximum temperature at the overload is reached).

    Fan Motor FLA is the amperage drawn at the motors full-load torque and horsepower. For Fan motors this is minimally affected by temperature and humidity so it doesn't change. Motors have this on their nameplate as well as the unit nameplate, compressors do not.

    FLA is also sometimes referred to as the Running Load Amperes and should not be confused with the Rated Load Amperes.

    For compressor FLA (a.k.a. Running Load Amperes) It can be obtained from the manufactures electrical performance data that displays the kW at various conditions of temperatures and pressures.

    With the compressors actual voltage, amperage and power factor, the kW can be calculated and then compared to the performance data at actual conditions to determine if the compressor amperage is what the manufacturer intended it to be.

    The FLA is determined by the motor manufacturer and is used to select the correct wire gauge, motor starter, and overload protection devices necessary to serve and protect the motor/compressor.

    For compressors, neither FLA or RLA is on the nameplate of the compressor. This is because the compressor manufacturer does not determine the actual application or conditions at which the compressor will be operated.

    LRA (Locked Rotor Amperage) is located on the compressor nameplate. LRA is the maximum current spike during a motor start. If the compressor motor was electrically fine, but mechanically locked, it would draw at or near the nameplate LRA.

    For troubleshooting PSC fan motors, the actual amperage (with access doors in place) should not be less than 25% or over 10% of the motors FLA on the motors nameplate.

    For troubleshooting PSC compressor motors:

    While operating, the actual amperage should not be greater than the RLA on the unit nameplate. The formula given by Yuma, LRA divided by 5 for RLA, then RLA times 0.8 for FLA, is an adequate guess for when the manufactures data is not readily available. A low compressor amperage by itself, does not indicate a compressor failure.

    If powered but not rotating (humming), the actual amperage should not be more or less than 10% of the LRA on the compressor nameplate. If <>10%, the compressor windings, line voltage or external components are at fault.

    Rotating or not, if the actual amperage is somewhere in between the RLA and LRA, then the compressor windings, line voltage or external components are at fault.

    References-
    http://www.achrnews.com/articles/115...-amperage-data

    https://books.google.com/books?id=eS...%20RLA&f=false

    http://iaeimagazine.org/magazine/199...ump-equipment/

  6. #6
    Join Date
    Jul 2012
    Location
    Bridgeton, MO, 'burb of St. Louis, Mo
    Posts
    7,846
    Post Likes
    Quote Originally Posted by penderway View Post
    An important note about FLA, RLA and LRA as they pertain to PSC (Permanent Start Capacitor) Compressors and PSC Fan motors.

    Compressor RLA (Rated Load Amperage) and Fan Motor FLA (Full Load Amperage) are located on the condenser or heatpump nameplate.

    Compressor RLA is the current drawn at the highest load conditions for which the compressor is rated to operate. Typically 115°F outside 80°/67° inside.

    The compressors internal overload will typically open at 1.5 times the Compressors RLA during continuous operation (or if the maximum temperature at the overload is reached).

    Fan Motor FLA is the amperage drawn at the motors full-load torque and horsepower. For Fan motors this is minimally affected by temperature and humidity so it doesn't change. Motors have this on their nameplate as well as the unit nameplate, compressors do not.

    FLA is also sometimes referred to as the Running Load Amperes and should not be confused with the Rated Load Amperes.

    For compressor FLA (a.k.a. Running Load Amperes) It can be obtained from the manufactures electrical performance data that displays the kW at various conditions of temperatures and pressures.

    With the compressors actual voltage, amperage and power factor, the kW can be calculated and then compared to the performance data at actual conditions to determine if the compressor amperage is what the manufacturer intended it to be.

    The FLA is determined by the motor manufacturer and is used to select the correct wire gauge, motor starter, and overload protection devices necessary to serve and protect the motor/compressor.

    For compressors, neither FLA or RLA is on the nameplate of the compressor. This is because the compressor manufacturer does not determine the actual application or conditions at which the compressor will be operated.

    LRA (Locked Rotor Amperage) is located on the compressor nameplate. LRA is the maximum current spike during a motor start. If the compressor motor was electrically fine, but mechanically locked, it would draw at or near the nameplate LRA.

    For troubleshooting PSC fan motors, the actual amperage (with access doors in place) should not be less than 25% or over 10% of the motors FLA on the motors nameplate.

    For troubleshooting PSC compressor motors:

    While operating, the actual amperage should not be greater than the RLA on the unit nameplate. The formula given by Yuma, LRA divided by 5 for RLA, then RLA times 0.8 for FLA, is an adequate guess for when the manufactures data is not readily available. A low compressor amperage by itself, does not indicate a compressor failure.

    If powered but not rotating (humming), the actual amperage should not be more or less than 10% of the LRA on the compressor nameplate. If <>10%, the compressor windings, line voltage or external components are at fault.

    Rotating or not, if the actual amperage is somewhere in between the RLA and LRA, then the compressor windings, line voltage or external components are at fault.

    References-
    http://www.achrnews.com/articles/115...-amperage-data

    https://books.google.com/books?id=eS...%20RLA&f=false

    http://iaeimagazine.org/magazine/199...ump-equipment/
    Nice post!


    If thinking was easy,
    everyone would do it!


    Regarding Russian Roulette; five out of six players think it is a safe, enjoyable game!

    "And I've been banned twice. What of it? If you aren't getting banned once every 3 years, you aren't trying." Brian8383

    "it's actually 90 right now in this shaded area of satan's butthole." - HVAC_marc

    “Don't believe signature quotes.” - George Washington

  7. #7
    Join Date
    Mar 2013
    Location
    Treasure coast, FL
    Posts
    11,466
    Post Likes
    Quote Originally Posted by penderway View Post
    An important note about FLA, RLA and LRA as they pertain to PSC (Permanent Start Capacitor) Compressors and PSC Fan motors.

    Compressor RLA (Rated Load Amperage) and Fan Motor FLA (Full Load Amperage) are located on the condenser or heatpump nameplate.

    Compressor RLA is the current drawn at the highest load conditions for which the compressor is rated to operate. Typically 115°F outside 80°/67° inside.

    The compressors internal overload will typically open at 1.5 times the Compressors RLA during continuous operation (or if the maximum temperature at the overload is reached).

    Fan Motor FLA is the amperage drawn at the motors full-load torque and horsepower. For Fan motors this is minimally affected by temperature and humidity so it doesn't change. Motors have this on their nameplate as well as the unit nameplate, compressors do not.

    FLA is also sometimes referred to as the Running Load Amperes and should not be confused with the Rated Load Amperes.

    For compressor FLA (a.k.a. Running Load Amperes) It can be obtained from the manufactures electrical performance data that displays the kW at various conditions of temperatures and pressures.

    With the compressors actual voltage, amperage and power factor, the kW can be calculated and then compared to the performance data at actual conditions to determine if the compressor amperage is what the manufacturer intended it to be.

    The FLA is determined by the motor manufacturer and is used to select the correct wire gauge, motor starter, and overload protection devices necessary to serve and protect the motor/compressor.

    For compressors, neither FLA or RLA is on the nameplate of the compressor. This is because the compressor manufacturer does not determine the actual application or conditions at which the compressor will be operated.

    LRA (Locked Rotor Amperage) is located on the compressor nameplate. LRA is the maximum current spike during a motor start. If the compressor motor was electrically fine, but mechanically locked, it would draw at or near the nameplate LRA.

    For troubleshooting PSC fan motors, the actual amperage (with access doors in place) should not be less than 25% or over 10% of the motors FLA on the motors nameplate.

    For troubleshooting PSC compressor motors:

    While operating, the actual amperage should not be greater than the RLA on the unit nameplate. The formula given by Yuma, LRA divided by 5 for RLA, then RLA times 0.8 for FLA, is an adequate guess for when the manufactures data is not readily available. A low compressor amperage by itself, does not indicate a compressor failure.

    If powered but not rotating (humming), the actual amperage should not be more or less than 10% of the LRA on the compressor nameplate. If <>10%, the compressor windings, line voltage or external components are at fault.

    Rotating or not, if the actual amperage is somewhere in between the RLA and LRA, then the compressor windings, line voltage or external components are at fault.

    References-
    http://www.achrnews.com/articles/115...-amperage-data

    https://books.google.com/books?id=eS...%20RLA&f=false

    http://iaeimagazine.org/magazine/199...ump-equipment/
    Don't mean to nitpick; but PSC stands for "permanent split capacitor"

    Everything else was spot on, though!

  8. #8
    Join Date
    Aug 2001
    Location
    Mechanicsville, Virginia
    Posts
    2,042
    Post Likes
    Quote Originally Posted by rc811002 View Post
    Nice post!
    Thanks, had some time to kill

    Quote Originally Posted by shellkamp View Post
    Don't mean to nitpick; but PSC stands for "permanent split capacitor"

    Everything else was spot on, though!
    Dang! and I can no longer edit it

  9. #9
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    7,049
    Post Likes
    Quote Originally Posted by penderway View Post


    Dang! and I can no longer edit it
    We'll let it slide this time

  10. #10
    Join Date
    Jan 2011
    Location
    Ward, Arkansas, United States
    Posts
    916
    Post Likes
    Good post, can I stamp that on my techs forehead?
    "Gentlemen. You can't fight in here. This is the War Room!"-Dr. Strangelove (1964)

  11. #11
    Join Date
    Mar 2021
    Posts
    8
    Post Likes
    Quote Originally Posted by penderway View Post
    FLA is also sometimes referred to as the Running Load Amperes and should not be confused with the Rated Load Amperes.
    For compressor FLA (a.k.a. Running Load Amperes) It can be obtained from the manufactures electrical performance data that displays the kW at various conditions of temperatures and pressures.
    Isn't FLA= Rated Load Amps and not Running Load Amps!!!

  12. #12
    Join Date
    Mar 2021
    Location
    Hendersonville NC
    Posts
    382
    Post Likes
    Quote Originally Posted by newoldtech View Post
    The LRA on my compressor was 102, and I read 15.5

    102 divided by 6 is 17. So its pretty close. I will remember it. Thanks.
    IN HEAT MODE OR COOL MODE? USSUALLY WITH CORRECT CHARGE AND NORMAL CONDITONS IN AC MODE YOU WILL HAVE HALF THE FLA AS YOUR RLA.. LRA/5=FLA FLA/2=RLA

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •