First day running service and I don't start school until next sept. Can you take pressures at the condenser and get accurate measurements when the lineset is 25-30'? Shouldn't a lot of readings be taken at the evaperator? The tech I was with said there were no schraders at the evaperator and that was his only access to the system. I'm still dumber than dumb and didn't want to question him on my first day but how do you know what is going on at the evaperator if you only measure pressure and temp at the condensor?
-
07-28-2008, 10:09 PM #2
Except for a few units, you won't have schrader fittings anywhere but at the condenser.
In school they will tell you to allow a 2 PSIG pressure frop on your vapor line.
Some systems you won't have that, others you will have moe then that.
Liquid line doesn't have as much as a presure drop.
Most charging charts are for measurements at the condenser.
To go into more would be more then allowed in the open resi forum.
Get your post count up to 15 and apply for pro membership. Then you can ask questions in the pro tech forum.
You may even want to tell the tech your working with about this site.
be fore warned though. It takes a thick skin sometimes. As some answers are given very sarcastically.
-
07-28-2008, 10:10 PM #3
The government works for me. I do not answer to them, they answer to me.
we need a few more sheep dogs to keep barking at the wolves,and the stupid sheep
A well-regulated militia, being necessary to the security of a free State, the right of the people to keep and bear arms, shall not be infringed.
-
07-28-2008, 10:11 PM #4
I only check pressure at the evaporator (if avaliable and usually not) only if I'm checking superheat or looking for a restriction. Connecting at the condenser is standard. Your pressures will be almost the same at the expansion device inlet as it is comming out of your condenser. And the same at the comprssor suction inlet as it will be comming out of your evaporator give a few pounds differance.
-
07-28-2008, 10:12 PM #5
Professional Member
- Join Date
- Sep 2005
- Location
- Texas
- Posts
- 2,793
so true beenthere but as the good book says, "iron sharpens iron"

GOOD LUCK NEWBIE!!!!
-
07-28-2008, 10:28 PM #6
Regular Guest
- Join Date
- Jul 2008
- Posts
- 7
Thanks guys, How would you feel if a guy on his first day was questioning what you were doing? I just wanted to ask somewhere to make sure what I was learning out the gate was correct.
-
07-28-2008, 10:31 PM #7
I am finding that all they do is check suction pressure & maybe feel the suction line.
They have a blank stare if you mention superheat & subcooling, & have nothing to take those line temps with! The first thing I did was put the thermo-sensors on both lines, preparing to to check both SH/SC.
Do they teach checking SH & SC in tech schools now?
How many don't have anything to check even the duct velocity, nor the static pressure.
The cooling season is short here in SW WI, perhaps that be part of it.(?)
- DarrellAOP Forum Rules:
Rules for Posting
Rules For Equipment Owners
Equipment Owners Find a Contractor HERE!
udarrell
-
07-28-2008, 10:33 PM #8
-
07-28-2008, 10:41 PM #9
The government works for me. I do not answer to them, they answer to me.
we need a few more sheep dogs to keep barking at the wolves,and the stupid sheep
A well-regulated militia, being necessary to the security of a free State, the right of the people to keep and bear arms, shall not be infringed.
-
07-28-2008, 10:53 PM #10
-
07-28-2008, 10:58 PM #11
The government works for me. I do not answer to them, they answer to me.
we need a few more sheep dogs to keep barking at the wolves,and the stupid sheep
A well-regulated militia, being necessary to the security of a free State, the right of the people to keep and bear arms, shall not be infringed.
-
07-28-2008, 11:05 PM #12
-
07-28-2008, 11:16 PM #13
Professional Member
- Join Date
- Sep 2005
- Location
- Texas
- Posts
- 2,793


Reply With Quote