    Dunham Bush NC25-4 upgrade to Director

    Anyone performed the Dunham Bush NC25-4 controller (obsolete- originally made by Danfoss) upgrade to the Dunham Dush Director controller.

    I have one on order thru DB, curious on ease of conversion and will it be worth the $$$$ spent

    I couldn't find a similar controller that was not oem to operate this chiller

    The NC25-4 stages all 3 screw compressors, 18 cond fans, loads/unloads the compressors from its software

    Air cooled chiller it is on is a ACDX170B with 3 60 hp screw compressors

    fatboy

  2. #2
    Join Date
    Jun 2008
    Location
    Baltimore,Md
    Posts
    17

    DB-danfoss upgrade

    I used to be the National Service Manager for Dunham Bush and this upgrade to the new controls will make all operations smoother and this upgrade is easy just be careful of terminal markings

  3. #3
    Join Date
    Mar 2001
    Posts
    740

    Allen A

    The upgrade is 3-4 weeks away from D/B

    School starts in 3 weeks, teachers in bldng in 1 1/2 weeks , chiller does entire 800 student school

    D/B says retrofit will take 30-40 hours

    GB at D/B is slammed and can't expedite

    I am considering temporary temp controls to at least get 2 comp running

    I have had great luck with this machine until the NC25 went sour, and don't want to scramble the screws

    thinking about a Hnywl T775 with fan cycling per circuit, unit has standard txv's

    not sure how to load/unload the solenoids and what the timing is to fully load

    probably a timer to load up to 50%-75%

    not sure if I need to energize fast unload solenoid at shutdown/staging off

    Am I on the right thinking track or asking for trouble

    I got the supt of schools riding me hard

    fatboy

  4. #4
    Join Date
    Jun 2008
    Location
    Baltimore,Md
    Posts
    17

    DB

    which model screw compressors are on chiller

  5. #5
    Join Date
    Mar 2001
    Posts
    740

    Allen A

    compressors are

    Hitachi SSCA075AR/COE10735

    fatboy

  6. #6
    Join Date
    Jun 2008
    Location
    Baltimore,Md
    Posts
    17

    hitachi

    with these screws you can use a w-7100 for screw chillers

  7. #7
    Join Date
    Jun 2008
    Location
    Baltimore,Md
    Posts
    17

    sorry to give complete answer.

    yes you do energize fast unload at shut down or any operating alarm

  8. #8
    Join Date
    Jul 2006
    Location
    The Great country of Texas
    Posts
    429
    Install a MCS panel from Micro Controls in Fla. Talk to James Mitchell. 239-694-0089. They have retro many DB's. One of the ex-DB guys works there.
    "I'm from Texas, what country are you from?"

  9. #9
    Join Date
    Aug 2000
    Location
    USA
    Posts
    4,995
    Agree, I have several D/B chillers upgraded to MCS. They all run pretty much flawlessly. Bet MCS is a 1/3 the price of the D/B crap.
    Quote Originally Posted by stickerhead View Post
    Install a MCS panel from Micro Controls in Fla. Talk to James Mitchell. 239-694-0089. They have retro many DB's. One of the ex-DB guys works there.
    Your poor planning does not constitute an emergency on my part!!!!

  10. #10

    inquiry re: d/b compressor

    Quote Originally Posted by Allen Anders View Post
    I used to be the National Service Manager for Dunham Bush and this upgrade to the new controls will make all operations smoother and this upgrade is easy just be careful of terminal markings
    hi allen...just want to ask if you're familiar with the d/b model mbt 44-1 with sp# mil-c-14370 or is there really such a model? have a friend who gave me the info and is offering to sell me a couple of units though i have yet to see them...they're belt driven by the way...any info or insight would be highly appreciated...another thing...if there is such a unit, would you happen to know where i can get a copy of its catalogue or manual?