07-26-2008, 05:18 PM #1
Regular Guest
- Join Date
- Jun 2008
- Posts
- 8
Where did the refrigerant go?
I have a customer who has a large back bar, about 9 evap coils on the system. We got a call its warm. I go check it out, and it has no refrigerant in system. Im thinking, this will be a easy leak find. I dump some gas in it and check for leaks, on all coils,TEV, sol etc. None found. I charge up the unit, 28lbs of refrigerant. So now its got me nervous. Only place I could not check was in the attic. This was 3 days ago, and it has not lost any refrigerant. The system has high and low pressure controls. Its got me baffled because I never ran into a completely empty system and no sign of leaks. No gas = big leak. It was working good, then bam, its warm, over night. At this point im thinking the one man company owner from the other company let it out? Its got me confused. Thoughts??
-
07-26-2008, 05:20 PM #2
What was your final micron reading before you charged the sytem back up?
-
07-26-2008, 05:51 PM #3
Regular Guest
- Join Date
- Jul 2008
- Location
- ATL
- Posts
- 56
Next time if you come across a flat system get nitrogen with some trase of 22in the system and get up to 150psi you will hear it even in attic.And unless some sees someone letting gas out of the system lets not ASSuME because next time someone could ASSuME that you did something like that.
-
07-26-2008, 05:56 PM #4
Regular Guest
- Join Date
- Jun 2008
- Posts
- 8
Oh yea, 440. It was going to be 4 hours till opening an cooler was @ 85 deg.
Was in a hurry.I figured for sure by morning it would be out again, so that early evening I went back to check on it and it was still full. 3 days later, still full.
I will be able to get in the first of next week. There is also plenty of dye in the system.
This is a recent customer and first time I worked on it. He said every few months this happens. No warning signs from cold to warm and the guy keeps coming back dumping refrigerant in it.
Is whats got me so confused is, 0 refrigerant with pressure controls, low pressure control set at 20 psi. A leak that leaks it all out in less then 24 hours is huge.
-
07-26-2008, 06:02 PM #5
Regular Guest
- Join Date
- Jun 2008
- Posts
- 8
-
07-26-2008, 06:03 PM #6
-
07-26-2008, 06:06 PM #7
Regular Guest
- Join Date
- Jun 2008
- Posts
- 8
-
07-26-2008, 06:14 PM #8
If you pulled 400 microns there is no leak..........period.
That leaves only 2 things that I can think of off the top of my head that would relieve the pressure on the system
The first is a relief valve that is popping and resetting - although those will typically reset well above 0 psig
The second is some knucklehead(s) huffing refrigerant to get high - although you think you'd see a dead body or 2 laying around after 30 lbs of inhaled refrigerant in their lungs.
-
07-26-2008, 07:07 PM #9
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,509
Does it have somekind of pressure relief on the system?
-
07-26-2008, 09:10 PM #10
Regular Guest
- Join Date
- Jun 2008
- Posts
- 8
-
07-27-2008, 12:44 PM #11
Member
- Join Date
- Dec 2005
- Location
- Rockhill South Carolina
- Posts
- 370
A low micron reading is good but it could be something that holds in a vacuum but not under pressure,so a micron reading is not all I would use.
-
07-27-2008, 03:04 PM #12
Banned
- Join Date
- Dec 2006
- Location
- Middle Tennessee
- Posts
- 11,347
*
locking refrigerant caps would be a start
system with no freon=get the nitrogen
tie a balloon on to the relief valve, it will pop the balloon if it dumps the charge
.