    Quote Originally Posted by beenthere View Post
    Add the amp requiements of the OD unit to that yet, and you could force youself to do an unrequired elecgtrical upgrade.
    If the OD unit and strips can be run together add in those BTUs. You are getting something for those amps.

    The COP curve will help pin down the BTUs, but be careful there. The DOE tests we ran to gen those numbers are unlikely to represent your specific situation. Its a ballpark, but better than nothing. If you root around on the net for the manufacturer standardized testing or check the archives I think there were some discussions about those limitations.

  2. #15
    Join Date
    Jul 2008
    Posts
    13
    Post Likes
    Thread Starter
    Quote Originally Posted by beenthere View Post
    Your heat pump will still need a strip heater to temper the air during defrost.
    I'd been wondering if the outside coils would would ever frost from the condensate being pulled from the outside air. I suppose the defrost cycle occurs more or less frequently depending on outside temp and RH. Does the HP run in cooling cycle to generate the defrost BTUs or do the outside coils have electric heaters in them for this purpose? How does the HP know when to defrost itself?

  3. #16
    Join Date
    Jan 2004
    Location
    PA
    Posts
    74,902
    Post Likes
    How much of a temp set back depends somewhat on the thermostat you use.

    The HP switches to cooling mode to defrost.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  4. #17
    Join Date
    Jan 2004
    Location
    PA
    Posts
    74,902
    Post Likes
    Quote Originally Posted by dac122 View Post
    If the OD unit and strips can be run together add in those BTUs. You are getting something for those amps.
    The point was if you over size the strips you can force your self to do a panel upgrade when its really not needed.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.