Need Bryant Economizer help
Ok guys, thrown into a job via national accounts that have all Bryant units on the roof, no literature but they have economizer board with 2- 9 volt batteries on them, I turn the outdoor controller on the economizer down but the damper doesn't move, units won't heat or cool so I know it is an economizer issue.Anyone have troubleshooting literature on these and are the boards junk, I turned the damper worm gear by hand and it moves back to one position so motor moves.
-
07-24-2008, 09:53 PM #2
Professional Member
- Join Date
- Nov 2004
- Posts
- 209
how about more info?model/serial #. is it a separate econo board?
AIRFLOW IS CRITICAL
-
07-24-2008, 10:42 PM #3
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,509
Man I haven`t seen one of those in years end switches and all huh.
-
07-25-2008, 06:09 AM #4
Professional Member
- Join Date
- Aug 2002
- Location
- manitowoc wisconsin
- Posts
- 4,687
The boards for those are so costly you should install new micrometal econmizers & forget fixing them.
Take your time & do it right!
-
07-26-2008, 09:05 AM #5
Professional Member
- Join Date
- May 2006
- Posts
- 16
Jumpering blue and gray on the economizer molex plug will get you mechanical cooling. The two 9 volt batteries were to shut the damper in the event of a power failure. I agree with the previous post. Too costly to repair.
Go to mechanical cooling(fan cycle,crankcase htr.,etc.) or reinvent the wheel.