Results 1 to 4 of 4
    Oct 2005
    Goodman 13 Seer Heat Pump
    This was Posted Earlier but was moved
    New Install--Outside unit and AHU--Heat Pump
    10 Degree Slit on Air Temp inside-Ret and Supply
    Superheat 10 Degrees--Tried Adjusting Charge--Superheat stayed 10 either way
    Unit not Cooling Properly--Need 15-18 Degrees across Evap Coil.
    R-22 System--Piston Metering Device.
    Mar 2001
    North Carolina
    It was moved to pro forum. You have replies there.
    http://hvac-talk.com/vbb/showthread.php?t=177454
    Read site rules. Since we aren't allowed to give DIY instruction in this forum.
    We can't give technical advice to a pro in this forum either.
    Oct 2005
    Smile Goodman 13 Seer Not Cooling
    The Unit has been Repaired--Due to a Leak on Installation--Too much Refrigerant was added back--Weighed in Charge and Now--15 Degree Superheat and 15 Degrees across Coil--10 Degree Subcooling--Thanks For all your Help!!!
