    Hopefully someone can help me troubleshoot my problem. My Carrier unit runs all the time during the day and sometimes falls behind keeping up with the set point on my T-Stat.

    Details listed below:
    4 Ton Single Zone System made by Carrier and installed in 1996
    Single Family Home 1975 Sq Ft two story cathedral ceilings

    Today’s Readings at 5:00 PM
    Oustide Air Temp 80 Degrees
    Suction Temp At Condenser – 59.2 Degrees
    High SideTemp At Condenser – 83.8 Degrees
    Suction Pressure – 66 psi.
    High Side Pressure – 255 psi.

    R-22 Freon
    I calculate my superheat at 20 Degrees

    This evening my return temp at the return grill was 64 degrees and the supply temp at a register was 56 degrees. Only 8 degrees differential

    Is this unit low on Freon? Or is there something else going on?

    Any help would be greatly appreciated.
    George

  2. #2
    Join Date
    Nov 2001
    Location
    Seattle, WA
    Posts
    7,989
    Post Likes
    Quote Originally Posted by GeorgeCJ View Post
    R-22 Freon

    This evening my return temp at the return grill was 64 degrees and the supply temp at a register was 56 degrees. Only 8 degrees differential
    So your house is at 64 degrees?
    "The American Republic will endure until the day Congress discovers it can bribe the public with the public's own money.
    - Alexis de Toqueville, 1835

  3. #3
    Join Date
    Feb 2008
    Location
    Western NC
    Posts
    2,504
    Post Likes
    Quote Originally Posted by GeorgeCJ View Post
    Hopefully someone can help me troubleshoot my problem. My Carrier unit runs all the time during the day and sometimes falls behind keeping up with the set point on my T-Stat.

    Details listed below:
    4 Ton Single Zone System made by Carrier and installed in 1996
    Single Family Home 1975 Sq Ft two story cathedral ceilings

    Today’s Readings at 5:00 PM
    Oustide Air Temp 80 Degrees
    Suction Temp At Condenser – 59.2 Degrees
    High SideTemp At Condenser – 83.8 Degrees
    Suction Pressure – 66 psi.
    High Side Pressure – 255 psi.

    R-22 Freon
    I calculate my superheat at 20 Degrees

    This evening my return temp at the return grill was 64 degrees and the supply temp at a register was 56 degrees. Only 8 degrees differential

    Is this unit low on Freon? Or is there something else going on?

    Any help would be greatly appreciated.
    George


    Your other thread was already closed.

    THIS IS NOT A DIY FORUM.

    Call a professional.

    Do not post it again.
    I fully support the military and the War on Terrorism.


    If you don't know, then don't do. If you don't know and still do, then be prepared to pay someone else a lot to undo what you did and then do it right.

    If you do know, then do. But do it right. Otherwise, you may not be doing it long.

  4. #4
    Join Date
    Mar 2004
    Location
    Illinois
    Posts
    6,959
    Post Likes
    Your last post was closed for obvious reason...no more or you'll be locked....out.