    Manitowac SY0505W

    At the Coke plant where I work we have a Manitowac SY0505W water cooled ice maker. This morning when it started a cycle I noticed a hammering or ticking sound. I went back to take a look and it sounded like water hammering or a valve-solenoid "fluttering" If I partially close the water valve to the machine it quits but did start again a few minutes later. Can anyone tell me what to look for? Would it be the water solenoid? Thanks for the help.
    ccnova

  2. #2
    Join Date
    Feb 2004
    Location
    Western New York
    Posts
    1,144
    Post Likes
    Water cooled manitowacs have this problem when they have a high water pressure feed. When they go into harvest the water valve throttles down fast, and when the next cycle starts the valve opens wide, then hunts. Both can cause a water hammer.

    Try installing a water regulating valve, and set it to around 35 psi. That seems to work for me.

    If this doesn't work, a new regulating valve might be needed.

    Good luck!
    Experience is what you have an hour after you need it.

  3. #3
    Join Date
    Mar 2007
    Location
    In the Conservatory with a Lead Pipe
    Posts
    12,072
    Post Likes
    If the pressure isn't out of sight do ya need someone to handle the warranty for ya
    “If You Can Dodge A Wrench You Can Dodge A Ball”

  4. #4
    Join Date
    Sep 2002
    Posts
    18,822
    Post Likes

    ccnova -

    Which Coke plant do you work in?

    PHM
    -----------


    Quote Originally Posted by ccnova View Post

    At the Coke plant where I work . . . .
    PHM
    --------
    The conventional view serves to protect us from the painful job of thinking.

  5. #5
    Join Date
    Dec 2007
    Posts
    45
    Post Likes
    Thanks for the replies everyone! baub I never thought about it but I bet you are right. We no longer bottle here but because we once did there are larger than normal water lines feeding the entire plant. If I remember right I think we have about 65 lbs of pressure everywhere. We will install a regulator and see what happens. Poodle Head Mikey, I work for Coca-Cola in Mitchell South Dakota. And itsiceman if we do I will move your name to the top of the list! Again thanks for the help everyone.
    ccnova

  6. #6
    Join Date
    Mar 2007
    Location
    In the Conservatory with a Lead Pipe
    Posts
    12,072
    Post Likes
    You should not hammer at 65 psi

    To bad I just blew through Nebraska

    I would have it changed

    Good Luck