Results 1 to 8 of 8
Thread: TXV
    malaysia
    TXV
    Any body can help me?
    The old TXV has totally under capacity, now I want to replace the new TXV and the problem is to select the new TXV match to the A/C system capacity.
    -to select TXV tonnage
    -compressor is 25 tons
    -A/C system for 1200 sq feet area
    melbourne aus
    txv
    g'day
    what is the make model and serial number of the a/c unit? that can help with getting a new one? what refrigerant? and pipe sizes? all this info will help
    in getting the correct txv
    generator
    Jun 2008
    South Carolina
    Your wholesaler should also be helpful in helping you select the correct one if you provide them with the information. Don't be shy in asking for catalogs. The Internet is also helpful, sporlan has a good site that can help you. As you probably know, selecting the right one is extremely important.
    Washington, DC
    How did you arrive at the conclusion the TXV is too small? In my experience, TXV's are the most wrongly accused parts of a refrigeration system.
    St Paul, minnesota
    Quote Originally Posted by mado View Post
    25 tons for cooling 1200 sq ft. !!! must have an extreme heat load
    Quote Originally Posted by superfittertech View Post
    that was my first thought!
    and what Pneuma said is true...add charge and d!ck with the TXV are the first thing that everybody does.
    good luck.
    malaysia
    g'day everyone....
    Actually this TXV problem is for control room at oil and gas platform.
    This A/C unit is custom made by manufacturer.
    Superfittertech: - sorry for that wrong info Room area (40ft x 50ft)
    - Control room
    Cool_tech :- the data is
    - Compressor type is Carlyle 06ET265660 (semi-hermetic)
    - R-22
    - Total capacity is 280789 Btu/hr
    - Sensible Capacity is 186931 Btu/hr
    - Cooling coil duty = 154 kW
    refer attachment:-
    Washington, DC
    Somethings are not adding up.
    So this is a 2000 square foot room?
    Compressor is rated at 23 tons
    Cooiling coil is 154kW X 3414 (BTU per KW) = 525,756 BTU/h or 43 tons
    Do you know how much air you put through the evaporator? Is it 100% outside air or recirculated return air?