    Choosing a boiler...

    I'm purchasing a home in Duluth, MN. The existing oil fired boiler has issues and needs either to be repaired or replaced. I'm considering scrapping the unit and installing an LP system, since natural gas is not available in the area... yet.

    The boiler feeds a baseboard system. I believe there are two or three existing zones.

    Sizing:
    I know I really should have a full blown heating test done. But, for now, I'm just looking for a solid estimate. The current oil boiler is 127,000 BTU. The house is 1800 sq feet. It's a split level. The split level (majority of sqft) was an addition, added in 1984.

    I also want to add an indirect hot water heater. It's currently electric. I may opt to add this later though due to budgetary reasons.

    After researching online, my gut is telling me that I'll need between 72,000 and 90,000 BTU.

    Boiler:
    I'm leaning towards the Weil-Mclain Ultra 105. It seems to have a lot of nice all-inclusive features. It's reasonably priced too. I'm also considering Buderus and Peerless, but am open to suggestions.

    My main concern with the boiler is the type. I want to make sure I'm getting the correct specs. Based on a telephone call with one contractor, I'm somewhat concerned about aluminum. He was definitely suggesting stainless. He noted issues with premature leaking and start-up leaks. Anyone have similar concerns?

    I guess my questions right now are:

    At the ~90,000 BTU range, is it safe to say I'm close?

    Does anyone have experience with the Weil-Mclain Ultra 105 in cold climates such as Duluth, MN?

    Are there other brands/models/types of boilers I should be considering?

  2. #2
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    We don't get as cold as you. But the Ultra does fine at our low temps of 0 or just under.
    If your baseboard is sized to heat your house at water temps under 200°F, the Ultra will work fine for you.
    As you probably saw, it comes with OD reset as standard.
    It can be programed to do a quicker or slow water temp increase as the application needs.
    As far as problems with the aluminum block. Nope. The Ultra comes with a 15 year warranty on the block. Most SS are 10, and 1 or 2 are 12 years.

  3. #3
    Join Date
    Jul 2008
    Posts
    21
    Post Likes
    Thread Starter

    Baseboard Sizing

    Quote Originally Posted by beenthere View Post
    If your baseboard is sized to heat your house at water temps under 200°F, the Ultra will work fine for you.
    Is it possible for me to determine whether the baseboards are sized for water temps under 200F myself?

  4. #4
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Yes and no.

    One way, is to see what temp the current boiler is set to.

    The other way, would be a heat loss, and then measure the amount of elecment.

  5. #5
    Join Date
    Jan 2002
    Location
    New Hampshire
    Posts
    1,285
    Post Likes

    yes

    First, you need to know the lengths in each room.

    Then you need to know the heat loss in each room.

    http://slantfin.com/heat-loss-software.html

    Divide the BTUs by the number of feet in the room, to get BTUH per foot required.

    Look up YOUR baseboard model for BTUH per foot at each water temperature, and select the temperature that matches your load.

    http://www.slantfin.com/product-fineline-30.html

    Noel

    p.s. I don't work for Slant/Fin (anymore, I moved back home).

  6. #6
    Join Date
    Jul 2008
    Posts
    21
    Post Likes
    Thread Starter
    Quote Originally Posted by Noel Murdough View Post
    First, you need to know the lengths in each room.

    Then you need to know the heat loss in each room.

    http://slantfin.com/heat-loss-software.html

    Divide the BTUs by the number of feet in the room, to get BTUH per foot required.

    Look up YOUR baseboard model for BTUH per foot at each water temperature, and select the temperature that matches your load.

    http://www.slantfin.com/product-fineline-30.html

    Noel

    p.s. I don't work for Slant/Fin (anymore, I moved back home).
    Thanks for outlining the process. Unfortunately, I don't live in the house (or even the state) yet. But, this will be the first thing I do when I get there. One question: is it easy to tell the make/model of baseboards? I have never dealt with them before.

    It's interesting that you mention Slant/Fin. My bother-in-law was touting Slant/Fin to me last night. Should I consider them? Are they all wall hanging? Or, do they have free standing boilers? The current boiler is freestanding next to the chimney. I figure it will be easiest to replace with a similar freestanding unit if I want to reuse the venting and plumbing as much as possible.

  7. #7
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    No mod/con boiler can reuse the venting of your existing boiler.
    They can't be vented into a regular chimney.

  8. #8
    Join Date
    Jul 2008
    Posts
    21
    Post Likes
    Thread Starter
    Quote Originally Posted by beenthere View Post
    No mod/con boiler can reuse the venting of your existing boiler.
    They can't be vented into a regular chimney.
    Good to know! Should I abandon the mod/con boiler for another type to reuse the chimney? Or, look to other venting options? Basically, does the additional work for venting and possibly re-routing plumbing outweigh the benefits of mod/con?

    If I don't go mod/con... what's the other type called? (Sorry, I'm new to this!)

  9. #9
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    mod/con boilers are direct vent. They vent either out the side of the building, or up through the roof in PVC pipe.
    Your hydronic piping can be reused to an extent. (minor alterations)
    Conventional would be what you would call other boilers, that are not condensing.

    Your best bet, is to get prices for both. Then decide what you can afford to put in, and use.

  10. #10
    Join Date
    Jan 2002
    Location
    New Hampshire
    Posts
    1,285
    Post Likes

    Mod Cons

    Depending on the water temperature that your system needs, a mod con MIGHT be an excellent choice.

    I like Slant/Fin baseboard better than the others, but there are a LOT of good boiler companies with good boilers. I also am in the stainless steel camp, vs. the aluminum boilers, on a mod-con. Aluminum can dissolve too quickly, if something goes wrong inside.


    Noel

  11. #11
    Join Date
    Jul 2008
    Posts
    21
    Post Likes
    Thread Starter
    Quote Originally Posted by beenthere View Post
    mod/con boilers are direct vent. They vent either out the side of the building, or up through the roof in PVC pipe.
    Can a mod/con boiler be placed in the center of the room and then have the PVC vent run up and over to the side?

    What about the chimney... can a PVC pipe be run up it?

  12. #12
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by Noel Murdough View Post
    Depending on the water temperature that your system needs, a mod con MIGHT be an excellent choice.

    I like Slant/Fin baseboard better than the others, but there are a LOT of good boiler companies with good boilers. I also am in the stainless steel camp, vs. the aluminum boilers, on a mod-con. Aluminum can dissolve too quickly, if something goes wrong inside.


    Noel
    SS can rot out pretty quick if something goes wrong inside.

    The OP can become a millionaire ovcer night if he buys the winning lottery ticket.


    Noel.
    How many Aluminum block mod/com boilers have you been involed with that dissolved? (not just heard about)

  13. #13
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by jrastama View Post
    Can a mod/con boiler be placed in the center of the room and then have the PVC vent run up and over to the side?

    What about the chimney... can a PVC pipe be run up it?
    Yes to both questions.

    All boilers have venting length limitations. Some ultras can have vents of 100'

  14. #14
    Join Date
    Nov 2001
    Location
    Moose Jaw, Saskatchewan, Canada Occupation:Interprovincial Plumber, Commercial Gasfitter Interests:
    Posts
    2,415
    Post Likes
    Quote Originally Posted by beenthere View Post
    SS can rot out pretty quick if something goes wrong inside.

    The OP can become a millionaire ovcer night if he buys the winning lottery ticket.


    Noel.
    How many Aluminum block mod/com boilers have you been involed with that dissolved? (not just heard about)
    I know of three. Also know of SS. Not enough attention is paid to water quality.
    I love my job, but paydays Thursday

  15. #15
    Join Date
    Jan 2002
    Location
    New Hampshire
    Posts
    1,285
    Post Likes

    What I see

    I can't elaborate, but what I've seen is in the lab of a boiler manufacturer.

    Let's just say that it didn't even have a model number, yet.

    How many mod-cons do you install and service in a year?

    Just asking.

    Noel

  16. #16
    Join Date
    Jul 2008
    Posts
    21
    Post Likes
    Thread Starter
    Quote Originally Posted by rich pickering View Post
    Not enough attention is paid to water quality.
    The area I'll be moving to has well water. Does that make a difference either way? Can I test the water periodically myself?

  17. #17
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Barely Half a dozen some years. 10 or 12 another. (If I was better salesman, it would be more)
    I have Ultras in both commercial and resi applications

    Going on 7th or 8th year for the second oldest Ultra I installed.
    The oldest the block was replaced because the freeze plugs started leaking.
    That was on city water.
    Got some on well water.

    Have heard people many times, say aluminum won't hold up.
    But, everybody I know personally that says that. Has never seen it himself.
    Or knows anything about the history of the install.

    I have a couple Pinacles in also, not vert impressed with them. Just one guy can carry them easier.

  18. #18
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    The water PH should be checked before installation.
    And yearly.

  19. #19
    Join Date
    Jan 2002
    Location
    New Hampshire
    Posts
    1,285
    Post Likes

    Best advice, yet

    I heartily agree on testing water in all boilers annually; at LEAST check the pH.

    Noel

  20. #20
    Join Date
    Jul 2008
    Posts
    21
    Post Likes
    Thread Starter
    Quote Originally Posted by beenthere View Post
    Your hydronic piping can be reused to an extent. (minor alterations)
    What alterations should I expect regarding the piping?

Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •