    Jackson, NJ
    Dual fuel. The aux only comes on with the HP during defrost.
    With electric aux, they run at the same time, when the HP can't handle the load by itself.
    Or, if the set point is reached outside, the aux runs exclusively if oil/gas. Right?
    Correct.
    The IAQ does have a droop point that either can run though also.
    2-stage HP IAQ question. How does the IAQ call for Y1 and Y2? Does it call Y2 at the same time as Y1 when it needs both stages or does it only close Y2 or Y1 but never both at the same time?
    Quote Originally Posted by badtlc View Post
    Both at the same time. If you have the manual, on page 23 there is a chart showing what is energized on what type of call. I've attached below...
    Quote Originally Posted by skunkiechris View Post
    I have the manual but cant find that. Is it in the installer's manual or the user's manual? That is a really useful table. Thanks.