Results 1 to 9 of 9
  1. #1
    Join Date
    Sep 2000
    Location
    Houston, TX, USA
    Posts
    19
    Post Likes

    How does this TXV installation grab you?

    Company #1 installed the HVAC in my new home one year ago. Had lots of problems so went with Company #2 for service. Company #2 traced a cooling problem to an issue with the TXV. Before tearing into the unit the prognosis was a) sensing bulb lost charge or b) debris in valve. Plan was to replace valve.

    What did he find? a) debris in valve, b) sensing bulb line very kinked and last but not least.........c) equalizer line cap still installed.

    Here is a photo of the valve with the cap on.

    As a home owner, what should I expect from Company #1?

  2. #2
    Join Date
    Feb 2008
    Location
    Western NC
    Posts
    2,504
    Post Likes
    Quote Originally Posted by Leaky Waders View Post
    Company #1 installed the HVAC in my new home one year ago. Had lots of problems so went with Company #2 for service. Company #2 traced a cooling problem to an issue with the TXV. Before tearing into the unit the prognosis was a) sensing bulb lost charge or b) debris in valve. Plan was to replace valve.

    What did he find? a) debris in valve, b) sensing bulb line very kinked and last but not least.........c) equalizer line cap still installed.

    Here is a photo of the valve with the cap on.

    As a home owner, what should I expect from Company #1?

    You shouldn't expect anything....

    But you could try contacting them. Make sure you have the bd vavle improperly installed, pictures of it, and the invoice from Company 2 stating the problem. Then you may be able to get something out of it.


    Most companies would rather calm you down and make you happy than to have their name tarnished. But don't expect a lot. Just contact em and see what happens. Do it tomorrow on Monday morning. Go in to their office and speak with owner if you want.


    Let us know how it turns out
    I fully support the military and the War on Terrorism.


    If you don't know, then don't do. If you don't know and still do, then be prepared to pay someone else a lot to undo what you did and then do it right.

    If you do know, then do. But do it right. Otherwise, you may not be doing it long.

  3. #3
    Join Date
    Feb 2007
    Location
    out in the country
    Posts
    637
    Post Likes
    Most TXV that I have installed have a plastic cap over the external equalizer line, the cap covers the entire flare it would be impossible to leave it on and install the external equalizer line.

    What kind of plug is in the tube? From the looks of it, I think most techs probably would not see it while installing it. Though I would hope they could trouble shoot a bad TXV.
    I never let schooling interfere with my education... Mark Twain

  4. #4
    Join Date
    Sep 2005
    Location
    Bay Area, CA
    Posts
    843
    Post Likes
    Why didn't you have the installing contractor come out and diagnose and fix there problem?
    Global Warming or: None like it hot
    No pleasure, no rapture, no exquisite sin greater... than central air. -Dogma

  5. #5
    Join Date
    Mar 2005
    Posts
    12,994
    Post Likes
    Quote Originally Posted by Leaky Waders View Post

    As a home owner, what should I expect from Company #1?
    Vasoline?

  6. #6
    Join Date
    Sep 2000
    Location
    Houston, TX, USA
    Posts
    19
    Post Likes
    Thread Starter
    Quote Originally Posted by ISOTHERMAL View Post
    Most TXV that I have installed have a plastic cap over the external equalizer line, the cap covers the entire flare it would be impossible to leave it on and install the external equalizer line.

    What kind of plug is in the tube? From the looks of it, I think most techs probably would not see it while installing it. Though I would hope they could trouble shoot a bad TXV.

    The plug appears to be made of the same material the line is made of. Brass I think, possibly copper.

  7. #7
    Join Date
    Sep 2000
    Location
    Houston, TX, USA
    Posts
    19
    Post Likes
    Thread Starter
    Quote Originally Posted by green jumper View Post
    Why didn't you have the installing contractor come out and diagnose and fix there problem?
    I lost confidence in the installer a long time ago. It is a long story that began with him installing a unit that was too large for the house. He had no idea what a Manual J or D were.

  8. #8
    Join Date
    Sep 2000
    Location
    Houston, TX, USA
    Posts
    19
    Post Likes
    Thread Starter
    Quote Originally Posted by iraqveteran View Post
    You shouldn't expect anything....

    But you could try contacting them. Make sure you have the bd vavle improperly installed, pictures of it, and the invoice from Company 2 stating the problem. Then you may be able to get something out of it.


    Most companies would rather calm you down and make you happy than to have their name tarnished. But don't expect a lot. Just contact em and see what happens. Do it tomorrow on Monday morning. Go in to their office and speak with owner if you want.


    Let us know how it turns out
    Here is how it turned out.

    I spoke with the installer today. He denies installing the valve with the cap in place but he has no alternative explanation. He agreed to refund me the $506.00 that I paid for the replacement of the valve, a filter drier and the labor.

  9. #9
    Join Date
    Jul 2000
    Location
    Northern Wisconsin
    Posts
    2,593
    Post Likes
    Congradulations.

    Life is good!
    Use the biggest hammer you like, pounding a square peg into a round hole does not equal a proper fit.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.