  1. #14
    Join Date
    Sep 2004
    Posts
    20
    I took the blower fan out and cleaned it really well. I also cleaned the evap and condenser. It embarrasses me to admit that the whole problem was a clogged condenser. The unit doesnt have a wire cage around it but more of sheet metal panels with slits so I couldn't see the coil. Since there was a 25° (alt 0176 thanks iraqveteran) TD across it I figured that it was doing a good job getting rid of heat. Also I did not think a clogged condenser would jack the pressures up to such an extreme. Unfortunately I left my temperature probe on another job the day before so I couldnt get the new superheat. On a good note I learned something from this call.

    Thanks for all the help guys!

  2. #15
    Join Date
    Dec 2007
    Posts
    26
    nlovas, good to hear you found the problem - dirty conden coil. Realy high head, high suction make sense.
    I am curious to learn why you got so much SC (25F)?
    Could it be overcharge as well that gives you 475 head and that SC?

    Quote Originally Posted by nlovas View Post
    I looked at a 12 year old 10seer Trane R22 split system today and could not solve the problem.
    Complaint: AC runs and cools but not sufficiently.
    First thing I did was to check the pressures: 90 and 475 on R22 system, 82 degree outside ambient.
    Then I took Superheat 38 and Subcool 25. BTW this is a distributer tube metering device so I know to concentrate on the Superheat.
    Next I took temperature differentials across the Condenser 25 and Evap 9.
    I looked around to see how dirty the coils other parts are and the coils did not look especially dirty so I did nothing to clean them. The furnace fan did have much buildup on the blades though.

    What I'm stuck on is that both pressures are very high and the superheat is very high also. Advise please.

    BTW how do I make a degree sign on the keyboard?

  3. #16
    Join Date
    Apr 2007
    Posts
    6,285
    No insulation on the suction line....


    Edit: better late then never...lol...even if dead wrong.

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event