  1. #1
    Join Date
    Apr 2008
    Posts
    31

    16 Seer Lennox unit

    I'm trying to get this 16 seer 2 stage condenser unit to run. This is in a brand new house trying to complete the start up. It has 3 wires coming out of the condenser instead of two. So it is a 2 speed compressor. The air hander blows out air, but the condenser does not run. According to the manual I have it wired up right. That seems kinda wierd though it is not running. So can anyone help me?

    Thanks

  2. #2
    Join Date
    Mar 2008
    Posts
    205

    Man I hope you're a pro

    Quote Originally Posted by lowridemazb2200 View Post
    I'm trying to get this 16 seer 2 stage condenser unit to run. This is in a brand new house trying to complete the start up. It has 3 wires coming out of the condenser instead of two. So it is a 2 speed compressor. The air hander blows out air, but the condenser does not run. According to the manual I have it wired up right. That seems kinda wierd though it is not running. So can anyone help me?

    Thanks
    otherwise......................................

  3. #3
    Join Date
    Mar 2005
    Location
    burlington county n.j.
    Posts
    9,709
    Quote Originally Posted by RomulanSpy View Post
    otherwise......................................

    won't be answered here............

  4. #4
    Join Date
    Jun 2008
    Location
    west point, ga.
    Posts
    328
    Quote Originally Posted by lowridemazb2200 View Post
    I'm trying to get this 16 seer 2 stage condenser unit to run. This is in a brand new house trying to complete the start up. It has 3 wires coming out of the condenser instead of two. So it is a 2 speed compressor. The air hander blows out air, but the condenser does not run. According to the manual I have it wired up right. That seems kinda wierd though it is not running. So can anyone help me?

    Thanks
    The best advice I can give is don't touch it without someone who knows what they are doing is there.That is a expensive unit to miswire and mess it up.

  5. #5
    Join Date
    Apr 2008
    Posts
    31
    Has anyone used one of these units before? I'm using a honeywell vision pro 8000 with one heat and one cool.

    I do this for a living but have only been in the field for 4 years. I think I'm doing pretty good for the little experience that I do have.

    Thanks for all the help

  6. #6
    Join Date
    Jun 2008
    Location
    west point, ga.
    Posts
    328
    Quote Originally Posted by lowridemazb2200 View Post
    Has anyone used one of these units before? I'm using a honeywell vision pro 8000 with one heat and one cool.

    I do this for a living but have only been in the field for 4 years. I think I'm doing pretty good for the little experience that I do have.

    Thanks for all the help
    Then you just answered your own question.

  7. #7
    Join Date
    Jul 2008
    Location
    Alabama
    Posts
    658
    Quote Originally Posted by lowridemazb2200 View Post
    Has anyone used one of these units before? I'm using a honeywell vision pro 8000 with one heat and one cool.

    I do this for a living but have only been in the field for 4 years. I think I'm doing pretty good for the little experience that I do have.

    Thanks for all the help
    Dude!! I could tell you , but then I would have to kill you.LOL

  8. #8
    Join Date
    Mar 2005
    Location
    burlington county n.j.
    Posts
    9,709
    one heat one cool on a 2 stage a/c unit...........




    houston we have a problem..........




    what diagram were you looking at that you thought you had it wired right??

  9. #9
    Join Date
    Jul 2008
    Location
    Alabama
    Posts
    658

    How many wires?

    Quote Originally Posted by lowridemazb2200 View Post
    It has 3 wires coming out of the condenser instead of two.

    Thanks

    Three wires ain't gonna cut it!

  10. #10
    Join Date
    Mar 2005
    Location
    burlington county n.j.
    Posts
    9,709
    Quote Originally Posted by superd77 View Post
    Three wires ain't gonna cut it!


    3 will for a xc16, they need to be hooked up right though......

  11. #11
    Join Date
    Apr 2008
    Posts
    31
    Yeah this is what the supervisor gave me was a one heat one cool thermostat on a 2 stage ac unit. I thought that was messed up. Why have the customer pay for a nice unit and not give them all the options the unit is capable of doing.

    I have the G61MPV series furnace.

    here is the wiring diagram that is in the furnace manual:

    tstat control term. strip outdoor unit
    w------W1
    r-------R
    g-------G
    c-------C------------------c
    Y2
    y-------Y1-----------------y

    That is how I have it wired up

  12. #12
    Join Date
    Jul 2008
    Location
    Alabama
    Posts
    658
    Quote Originally Posted by t527ed View Post
    3 will for a xc16, they need to be hooked up right though......

    Three won't work, Dude!!! It will never go into high speed!!! Especially if you don't hook up the blue wire.

  13. #13
    Join Date
    Jun 2008
    Location
    west point, ga.
    Posts
    328
    Quote Originally Posted by lowridemazb2200 View Post
    Yeah this is what the supervisor gave me was a one heat one cool thermostat on a 2 stage ac unit. I thought that was messed up. Why have the customer pay for a nice unit and not give them all the options the unit is capable of doing.

    I have the G61MPV series furnace.

    here is the wiring diagram that is in the furnace manual:

    tstat control term. strip outdoor unit
    w------W1
    r-------R
    g-------G
    c-------C------------------c
    Y2
    y-------Y1-----------------y

    That is how I have it wired up
    A pro 8000 will do anything you want it to except doing flips.Read the directions there not only there to fill the box.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event