Thread: Warm Master Bedroom
-
07-18-2008, 01:44 PM #1
Regular Guest
- Join Date
- Apr 2006
- Posts
- 80
Warm Master Bedroom
I had a new infinity 16 seer 4 ton 2 stage v/s heat pump put in my 2000sq foot home in Dallas Texas. The company did do a manual j test. The only problem I am having is the master bed room is still warm. It is the furthest room from the unit. The run is about 40ft long. When the unit is on high it cools the room fine. When it is on low the room gets warm. The unit runs on low 2/3 of the time, so the room is warm 2/3 of the time. The other parts of the home is fine, any suggestions?
-
07-18-2008, 01:52 PM #2
Air balance to provide comfort.
Merry Christmas

-
07-18-2008, 08:23 PM #3
If they did a room by room Manual J they should know the needed cfm, are you getting it? As jrbenny says have an air balance done.
Ask your contractor for the load calc and room cfm's.
-
07-18-2008, 11:37 PM #4
Regular Guest
- Join Date
- Mar 2008
- Location
- Central Maryland
- Posts
- 246


Reply With Quote