    Static Pressure

    I've read here to take statis pressure readings berfore the evap coil and after the filter on a furnace. If you were checking a evap air handler, would you test further doen stream to avoid VP?
    What was I thinking??? I never do that again!!!

  2. #2
    Join Date
    Jun 2005
    Location
    SW Wisconsin
    Posts
    4,973
    The positive tip reading goes before the evap coil while the negative tip goes after the filter & before the blower on a furnace is the External Static Pressure (ESP) reading; the reading on which mfg'ers rate equipment.

    If you know the initial drop through the filter, you could remove the filter, because as the filter loads its PD drop will keep increasing.

    When you check pressure drop across any device, including evaporator coil, you check pressures upstream & downstream of the device.

    The static pressure tip, when use correctly, is designed to measure static not Velocity Pressure (VP).

    It is good to design to retain as much velocity pressure as possible, because the more velocity is restricted (due to too small - high FR ducting) in relationship to CFM flow volume - static pressures will increase.

    http://www.udarrell.com/external_sta..._readings.html
    - Darrell

  3. #3
    Join Date
    Aug 2006
    Location
    Dallas (Plano), TX
    Posts
    168
    And are these 2 statements thus correct for a heat pump:

    The measurement points are after the blower motor and before the evap coil?

    If a filter is part of the unit, then meaure before the filter, and, look for a manufacturer's foot note (something like "Max ESP includes allowance for wet coil and standard filter")?

    Thank you.

    Bill

  4. #4
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,903
    Air handler. Between air filter and coil, and in supply plenum. Check foot notes for air filter allowances.
    On heat pumps. You must also look for foot notes on the strip heaters.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event