    Quote Originally Posted by mikelcs View Post
    i didn't see the /2 on the original post- i got that now
    Your right. He doesn't have that psrt of the formula in his.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  2. #28
    Join Date
    Mar 2005
    Location
    reading PA
    Posts
    20
    sorry about that...

  3. #29
    Join Date
    Jun 2006
    Posts
    294
    Checking my tables, I find that the formula is OK for WB temps >64 deg, indoor DB around 80 and ambient temps > 80 which makes it a rule of thumb formula.
    Since it doesn't take account of indoor DB it is especially limited.

  4. #30
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,773
    Since air at 64°F wet bulb has the same BTU at 74°F DB, that it does at 80°F DB, or 90°F DB ( 29.31 BTUs per pound of air, at sea level).
    What allowance do you think it needs for indoor dry bulb. Its the same load.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  5. #31
    Join Date
    Jun 2006
    Posts
    294
    Well since my charts show at 64 WB and outdoor ambient = 85 deg a range of 8 to 14 degrees SH for indoor DB range from 70 to 90 deg DB, The enthalpy of the 90 deg air and the 70 deg air differ by the sensible heat , so WB is close but not an exact indicator of enthalpy.

  6. #32
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,773
    The only difference, is the RH.
    It is the same amount of heat in the air at 70, as at 90.

    Plus. My SH slide charts don't use indoor DB either.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  7. #33
    Join Date
    Jun 2006
    Posts
    294
    My bad,
    Upon looking into this more, it is clear, as you say, that the enthalpy is practically independent of DB and virtually depends on WB alone.
    That, however doesn't say that the same input (WB) enthalpy into the A coil yields the same SH, since as you know at 90 the increase in sensible heat is offset by the decrease in latent vs 70 deg and maybe more heat is transferred at 90 deg since the average delta T is between the coil and the air is higher. However, more may be at play here.
    Just my $.02.

  8. #34
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,773
    At 90° indoor temp, and 64°WB, the RH is much lower, so you do have a much lower SH. Because you are removing more sensible heat. Then at 80° ID DB and 64° WB. At the same outdoor temps.
    But chance the OD drybulb, and the Target SH jumps.

    ID Wb of 64.
    At 90° OD, 11°SH.
    At 80° OD, 16°SH.
    At 70° OD, 21°SH.

    Manufactorurer specific charts may show slightly higher or lower. But will have a =or- tolerence.
    Using the formula on one of those units, is no different then using another brands slide chart on it.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

Page 3 of 3 FirstFirst 123

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event