target superheat
so ive seen a number of target superheat charts around but am wondering a calculation ive recently stumbled upon. wet bulb times 3,minus 80, minus outdoor ambient temp.. just wondering if most use a standard chart, try and go by what is on/in the odu, or mabey this calculation? any input is welcome...
-
07-18-2008, 12:51 AM #2
If the unit has a charging chart I use it.
If it doesn't and its a fixed metering device, I use that formula.
-
07-18-2008, 12:55 AM #3
Do you use outdoor DB or WB?
I fully support the military and the War on Terrorism.
If you don't know, then don't do. If you don't know and still do, then be prepared to pay someone else a lot to undo what you did and then do it right.
If you do know, then do. But do it right. Otherwise, you may not be doing it long.
-
07-18-2008, 01:07 AM #4
Outdoor DB.
-
07-18-2008, 06:19 PM #5
Same here. I use that formula, unless I have a manufacturers chart to go by.
-
07-18-2008, 06:20 PM #6
Do you guys take wb at return and supply and then average them?
-
07-18-2008, 06:36 PM #7
Professional Member
- Join Date
- Mar 2008
- Posts
- 657
is there a rule of thumb SH? i've read nothing below 8 and nothing above 30 true?
"The things you own end up owning you. "
Tyler Durden
-
07-18-2008, 06:57 PM #8
-
07-18-2008, 06:58 PM #9
if it's in the unit I use that, otherwise I use Trane's sliderule.
You can't fix stupid
-
07-18-2008, 08:00 PM #10
-
07-18-2008, 08:20 PM #11
-
07-18-2008, 08:26 PM #12
-
07-18-2008, 08:29 PM #13
seems like I have heard others say they take both and then average them to account for "mixing" I have just been doing return only, but tested a few by averaging, not a huge difference but about 2-3 degrees between methods. What is your theory of reading close to db if close to coil?