    Confused Heat and Cool simultanously - efficiency

    Hi,

    I'm having an HVAC system designed for a commercial building. We have a meeting room, offices and front lobby. The mechanical engineer told me that we cannot use one unit for all areas and zone it since the meeting room can get hot when many people are in, while the lobby can get cold. So a single unit cannot serve both zones. This makes sense, but under this scenario we are going to have cooling on one room and heating on the next room. It sounds terribly inefficient.

    Does anyone has a suggestion for a more efficient method?

    Thanks,

    Grumit

  2. #2
    Join Date
    Dec 2007
    Location
    Southern, CA
    Posts
    520
    Hold the meetings in the lobby? Tough to say without a lot more info, listen to the engineer.

  3. #3
    Join Date
    Mar 2003
    Posts
    7,249
    Not sure of your configuration, but there are at least two systems available that can offer you individual room control, and simultaneous heating/cooling. Daikin is one and Mitsubishi City Multi is the other. Each is a good system, with many features and energy recovery to allow simultaneous heating/cooling. They are extremeyl quiet, and very energy efficient, although for some contractors and engineers, they just don't get it. We have installed a bunch and they work great. There are others here who have had similiar results.

  4. #4
    Join Date
    Nov 2006
    Location
    Bay Area, California
    Posts
    12
    Thank you flange, I'll suggest these options.

  5. #5
    Join Date
    Sep 2007
    Location
    Yuma, Arizona
    Posts
    252
    It's not uncommon to run Cooling and Heating systems simultaneously. I have a building cooled by a chiller using vavs with reheats in them. While the chiller is running the boilers run pretty much most of the day to warm up cool spots and also help dehumidify. Many large and small buildings operate this way.

  6. #6
    Join Date
    Nov 2003
    Location
    Rochester, New York
    Posts
    392
    Its absolutly possible. VAVS with reheats is all you need. As said before, it will reheat the air dehumidy and it goes along its merry way. This is common practice in well designed office buildings. I would look for a new Engineer if this is all he/she has.

  7. #7
    Join Date
    Nov 2006
    Location
    Bay Area, California
    Posts
    12
    > Hold the meetings in the lobby?
    Can't do that!-)

    I've listened to the engineer. I understand this is the straightforward and conventional way, but I'm not happy since it's not efficient.

    Meeting room is about 400 SF. Lobby and office area is about 2000 SF. Stand alone building.