    Hi, i'm new to this forum as well as this industry. Just out of grad school i've joined this HVAC contracting firm and have a lot of unanswered questions. To start with about the psychrometric charts....

    Suppose i have outside air conditions of 80*f DB and 70*f WB / indoor conditions needed are 56*f DB and 55*f WB. How do i know the Apparatus dew point from the chart?

  2. #2
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Right side of chart has dew point.

  3. #3
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,847
    Post Likes
    Quote Originally Posted by BengalCooled View Post
    Hi, i'm new to this forum as well as this industry. Just out of grad school i've joined this HVAC contracting firm and have a lot of unanswered questions. To start with about the psychrometric charts....

    Suppose i have outside air conditions of 80*f DB and 70*f WB / indoor conditions needed are 56*f DB and 55*f WB. How do i know the Apparatus dew point from the chart?
    First of all, let's see if you understand what the apparatus dew point is. The numbers you gave for the indoor conditions sound like discharge air conditions, not indoor environmental conditions. At 56^F DB, 55^WB, the relative humidity is ~94%. These are not human comfort conditions.

    Apparatus dew point (ADP) is the dew point temperature of the cooling coil, which should be below the dew point of the return air entering the cooling coil. To determine ADP, you can use the psychrometric chart. Establish your return and supply statepoints on the chart, then draw a straight line through both points until it hits the saturation curve (the "instep") on the left side of the chart. Mark where it hits the curve, that's the ADP. It will typically be below the discharge air temperature.

    ADP is also known as Effective Coil Temperature (ECT). The dew point and the sensible temperature are the same, since ADP/ECT represents the moisture in the air being in a saturated state. ECT/ADP is useful for calculating coil bypass factor, to see to what extent air passing over the coil is left unaffected by the cooling coil.

  4. #4
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Maybe he's ripening bannas with 100% outdoor air, so they can call them fresh ripened.

  5. #5
    Join Date
    Jul 2008
    Location
    Bangalore, India
    Posts
    13
    Post Likes
    Thread Starter
    Quote Originally Posted by beenthere View Post
    Maybe he's ripening bannas with 100% outdoor air, so they can call them fresh ripened.
    he he thanks it was just a problem i was solving, not allowed to handle real life situations yet.
    By the way i checked and found the 80,70*f has 94 gr/lb of moisture while the 56,55*f had 64 gr/lb of moisture. Though the relative humidity % is increasing the total moisture content is decreasing. Won't it be comfortable?????
    Last edited by BengalCooled; 07-17-2008 at 11:23 PM. Reason: grammar

  6. #6
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    No, the 55,56, is 94 or 95% RH, it would be a sweat box in that eviroment. Your body can't cool down by persperation, it it can't evaporate

  7. #7
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,847
    Post Likes
    Quote Originally Posted by BengalCooled View Post
    he he thanks it was just a problem i was solving, not allowed to handle real life situations yet.
    By the way i checked and found the 80,70*f has 94 gr/lb of moisture while the 56,55*f had 64 gr/lb of moisture. Though the relative humidity % is increasing the total moisture content is decreasing. Won't it be comfortable?????
    Imagine being outside on a foggy day at 55^F with nothing on but a t-shirt, cargo shorts, and flip flops.

    Comfortable? I think not.

  8. #8
    Join Date
    Jul 2008
    Location
    Bangalore, India
    Posts
    13
    Post Likes
    Thread Starter

    thanks a ton

    Got it thanks people................

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •