low pressure side indicates vacuum while charging
Hey guys looking for some help.Been a residential installer for 15 years, recently switched to service due to lack of new construction. So I,m doing an initial start up and charging a newly installed ruud condensor and coil. 30 feet of lineset so I know it will need alittle R-22. Ilook at the gauges to find the suction side is reading a vacuum.I assumed this meant I had a restriction somewhere. Took the cover off the indoor coil and found that 3 of the 6 capillary tubes are cold and 3 are warm. when I removed my gauges I found the suction side released nothing when I depressed the schader. After reclaiming the gas I cut the suction line outside and ran 200 psi of nitrogen thru the high side and it blew freely out of the open line.What do I have here a restriction in the coil, a bad txv, or am I all together wrong and missing something else. Any help would be greatly appreciated.
-
07-15-2008, 09:55 PM #2
Professional Member
- Join Date
- Mar 2005
- Location
- Houston, Texas
- Posts
- 11,653
You're headed in the right direction. We can't give you a lot of tips in the open forums.
-
07-15-2008, 09:57 PM #3
I do think you are missing something.......FREON
What was the high side pressure reading?If you can't do it right.....Don't do it!!
-
07-15-2008, 10:11 PM #4
New Guest
- Join Date
- Jul 2008
- Location
- vineland new jersey
- Posts
- 3
Don't think I'm missing something as simple as freon,system was evacuated and compressors' charge was let go. Like I said the lineset was only about 30 feet in length. It should have shown something on the gauges. I'm new to this site so if I'm posting this question in the wrong place to expect an answer please let me know where I should post it.
-
07-15-2008, 10:17 PM #5
Professional Member
- Join Date
- May 2006
- Posts
- 281
As Wrangler said, your headed in the right direction. Site rules forbid us to be more specific in the open/residential forums. Get 15 posts under your name and apply for pro status, then ask your question again in the pro forum section for more detailed troubleshooting..
whaaaaa, you let all the smoke out
-
07-16-2008, 02:18 AM #6
You don't say anything about the head pressure.
The outdoor temp, or the indoor temps.
Wouldn't be the first unit that came from factory with only have its charge, or less.
Had units already that had a leak in the condenser from the factory. They ran in vacuum also.
So what was your head pressure and outdoor temp.
-
07-16-2008, 07:31 PM #7
Professional Member
- Join Date
- Jul 2008
- Posts
- 33
-
07-17-2008, 08:37 PM #8
New Guest
- Join Date
- Jul 2008
- Location
- vineland new jersey
- Posts
- 3
upon further inspection of the TXV I found my problem. Cleaning that little booger out really sucked in a 120 degree attic!! I sure do miss the much easier to clean piston. Thanks to all for your help.