Results 1 to 9 of 9
  1. #1
    Join Date
    Jul 2008
    Posts
    1
    Post Likes

    3 ton smaller than 2 ton???

    I got a Carrier heat pump installed last year that was supposed to be a 2 ton unit (for downstairs). I just got another Carrier heat pump that is supposed to be 3 tons (for upstairs) but it is shorter than the 2 ton unit (same width and depth on both).

    2 ton unit: model # 25HNA624A300
    3 ton unit: model # 25HNA636A300

    Can a 3 ton unit be smaller than a 2 ton unit???

  2. #2
    Join Date
    Jul 2006
    Location
    Virginia
    Posts
    7,669
    Post Likes
    yes some units have a double row of coils in the condensor and some have a single row

  3. #3
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,836
    Post Likes
    Quote Originally Posted by catmanacman View Post
    yes some units have a double row of coils in the condensor and some have a single row
    That's the reason,if you don't understand the double row coil,it's double thickness ,compared to single,so the three ton has more outdoor coil,in a shorter cabinet.

  4. #4
    Join Date
    May 2007
    Location
    DC Metro Area (MD)
    Posts
    3,374
    Post Likes
    Cabinet size isn't always indicative of size. I've seen small, large-tonnage units before.

  5. #5
    Join Date
    May 2007
    Location
    Naples, Fl
    Posts
    889
    Post Likes
    I'm not saying a word.

  6. #6
    Join Date
    Jul 2008
    Location
    Rydal,Ga
    Posts
    84
    Post Likes

    Is it a Builders Grade ???

    Is it a Builders Grade ???

  7. #7
    Join Date
    Sep 2007
    Location
    southern IN
    Posts
    527
    Post Likes
    No, those are both 16 seer heat pumps and yes the three ton is shorter
    The first man gets the pearl, All the second gets is the shell

  8. #8
    Join Date
    Jul 2008
    Location
    Alabama
    Posts
    682
    Post Likes
    Quote Originally Posted by adrianf View Post
    I'm not saying a word.


    Go on. Say it!! Size does what??LOL

  9. #9
    Join Date
    Jun 2008
    Location
    Morgantown, WV
    Posts
    140
    Post Likes
    The model number tells you the capacity.
    See the 24 before the A300 in the first one?
    See the 36 before the A300 in the second one?
    That is capacity in BTU/hr times 1000 so you have one 24,000 btu and one 36,000 btu condenser.
    One ton of air conditioning = 12,000 BTU/hr....or the amount of heat it takes to melt 2000 pounds (one ton) of ice in 24 hours.

    Size changes. Believe the model number for capacity.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.