    Thermostat ? for 2 stage system

    Posted questions about our A/C system over the past few weeks and another question crossed my mind as I was doing some more research.

    Since we have a 2 stage system trane xl16i, do we need a thermostat that has a 2 stage option? What is the purpose/advantage of a thermostat with a setting for 2 stage cooling? Our current thermostat does not have a 2 stage option

  2. #2
    Join Date
    Apr 2007
    Posts
    626
    Post Likes
    whats the question, the suspense is killing me.

  3. #3
    Join Date
    Dec 2002
    Location
    Arizona
    Posts
    4,480
    Post Likes
    Quote Originally Posted by aintitfun View Post
    whats the question, the suspense is killing me.

  4. #4
    Join Date
    Jun 2007
    Location
    Round Rock
    Posts
    4,744
    Post Likes
    It's kinda a self answering question. If you only have a 1 stage thermostat and a 2 stage a/c. It can only run 1 stage of the system. So 1 entire stage will never be used, which is a waste of the money you spent on it. If you're not gonna buy the thermostat, why did you buy the equipment. The heater will switch automatically unless you cut the jumper on the board. You will either run on "high" or "low" capacity depending on how it is wired.

  5. #5
    Join Date
    Apr 2007
    Posts
    626
    Post Likes

  6. #6
    Join Date
    Dec 2006
    Location
    Northern VA
    Posts
    389
    Post Likes
    Quote Originally Posted by bmathews View Post
    It's kinda a self answering question. If you only have a 1 stage thermostat and a 2 stage a/c. It can only run 1 stage of the system. So 1 entire stage will never be used, which is a waste of the money you spent on it. If you're not gonna buy the thermostat, why did you buy the equipment. The heater will switch automatically unless you cut the jumper on the board. You will either run on "high" or "low" capacity depending on how it is wired.
    OR

    Both stages are coming on at the same time and running at full capacity all the time.

  7. #7
    Join Date
    Jan 2008
    Posts
    81
    Post Likes
    Thread Starter
    Quote Originally Posted by bmathews View Post
    It's kinda a self answering question. If you only have a 1 stage thermostat and a 2 stage a/c. It can only run 1 stage of the system. So 1 entire stage will never be used, which is a waste of the money you spent on it. If you're not gonna buy the thermostat, why did you buy the equipment. The heater will switch automatically unless you cut the jumper on the board. You will either run on "high" or "low" capacity depending on how it is wired.
    You should be asking my installer that ?....I'm doing all this damn research because my brand new ac is not working properly. thanks for the info. I'm trying to figure out why THEY didn't install a 2 stage t-stat. don't need the heat info, as we have baseboard hot water..

  8. #8
    Join Date
    Apr 2007
    Posts
    626
    Post Likes
    No YOU should be asking your installer that.

  9. #9
    Join Date
    Apr 2007
    Posts
    626
    Post Likes
    Bottom line is, have them come out and install a 2 stage stat. That is a 2 stage unit, no other way is acceptable, My guess is they may only have a 2 conductor wire ran to the outdoor unit, which they will need at least three conductors.

  10. #10
    Join Date
    Jan 2008
    Posts
    81
    Post Likes
    Thread Starter
    Quote Originally Posted by aintitfun View Post
    whats the question, the suspense is killing me.
    I though they were spelled out..but i'll make it easier

    1. do we need a thermostat that has a 2 stage option?

    2. What is the purpose/advantage of a thermostat with a setting for 2 stage cooling?

  11. #11
    Join Date
    Dec 2002
    Location
    Arizona
    Posts
    4,480
    Post Likes
    You may have a 2 stage thermostat, but it is not set up correctly. Without a 2 stage thermostat your 2 stage system will only run on 1 stage, you paid for two.

  12. #12
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    A complete waste of money to get a 2 stage A/C, and only running it on a single stage stat.

    What is the brand and model number of your stat.

  13. #13
    Join Date
    Aug 2007
    Location
    Northern VA 38 degrees N by 76 degrees W
    Posts
    5,115
    Post Likes
    Your unit is more than likely mis-wired. You have a zoning panel and that will control your stages if wired correctly. From your previouse posts it is not wired correctly.

  14. #14
    Join Date
    Jan 2008
    Posts
    81
    Post Likes
    Thread Starter
    it is a honeywell pro 4000. The system does have a zone panel...does that mean we don't need the 2 stage tstat? Or, will the 2 stage tstat provide better control even with the zone panel?

    Lastly, I've seen that honeywell has a stat that appears to allow you program fan speed...will this help us solve the problems?

    thanks in advance for all your time and suggestions over the past 2 weeks.

  15. #15
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Ah, you have a zoned system.

    With many zone panels. The zone panel controls the staging.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •