    cfm for ac

    about a year ago i had a goodman furnace 70,000 btu and heatpump 3 ton put in. they set the cfm to high 1449 cfm. is that to high? medium is 1192. i know from being on this sit it should be about 400 cfm per ton. i have about a 21 degree drop at the a coil. is there something i dont understand? should it be at 1449cfm or should i call someone out to to look at it and set it to 1192 if need be? my furnace is GMH95 0703BXA and here is a link for the cfm http://www.goodmanmfg.com/Portals/0/pdf/SS-GMH95.pdf thank you chris

  2. #2
    Join Date
    Jul 2008
    Location
    Denver, CO
    Posts
    4,379
    Post Likes
    Yes for a heat pump 400 CFM per rated nominal ton is correct, and a 21 degree drop is also good sounds like your running ok. I would not worry about it every manufature has it's own specifications

  3. #3
    Join Date
    Jun 2007
    Location
    louisville ky
    Posts
    107
    Post Likes
    Thread Starter
    Quote Originally Posted by Tiger93rsl View Post
    Yes for a heat pump 400 CFM per rated nominal ton is correct, and a 21 degree drop is also good sounds like your running ok. I would not worry about it every manufature has it's own specifications
    do you think i could have it turned down so it is not so loud? i sit right next to the intake and the furnace is right on the other side of the wall. if i could have it turned down it would be great but i dont want to call someone out and have them say it is were it need to be and pay a service call for nothing.

  4. #4
    Join Date
    Apr 2007
    Posts
    626
    Post Likes
    I would like to see it set at 1192 if it were mine. Does your coil have a txv?

  5. #5
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,835
    Post Likes
    Take note that the fan data you posted,shows cfms at various ESP(External Static Pressures),so wihout testing the ESP,there's a wide range of cfms,depending on the ESP(think resistance to air flow,of ducts,filter,etc.).


    Based on the temperature drop,I'd guess your cfns cold be on the low side,or within proper range.Get a Pro that can test ESP and set the correct speed.


    Read here for an option to reduce noise; http://www.hvac-talk.com/vbb/showthread.php?t=176333

  6. #6
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    I doubt your getting the 1449 CFM with a 21°F temp diference on a 3 ton unit.

    Its a year old now. Time for a service check anyway. Have them check and adjust blower speed if needed.

  7. #7
    Join Date
    Jun 2005
    Location
    SW Wisconsin
    Posts
    6,627
    Post Likes
    Supposedly, they like to use 450-cfm per/ton, on heat pumps. That would be 1350-cfm for a 3-ton HP.

    It is not delivering 1449-cfm or 483-cfm per/ton, as stated; 21-TD indicates being on the low CFM side, unless you have a low indoor humidity factor.

  8. #8
    Join Date
    Jun 2007
    Location
    louisville ky
    Posts
    107
    Post Likes
    Thread Starter
    Quote Originally Posted by aintitfun View Post
    I Does your coil have a txv?
    yes

  9. #9
    Join Date
    Jun 2007
    Location
    louisville ky
    Posts
    107
    Post Likes
    Thread Starter
    Quote Originally Posted by beenthere View Post
    I doubt your getting the 1449 CFM with a 21°F temp diference on a 3 ton unit.

    Its a year old now. Time for a service check anyway. Have them check and adjust blower speed if needed.
    is a 21°F temp drop what it should be?

  10. #10
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Goodman has a listing of temp differences at different CFMs.
    But you need both the outdoor unit and indoor coil model number.

    My guess, is your moving around 1050 to 1100 CFM.

    Your duct system may be too restrictive for your blower to move the 1449 set CFM.

  11. #11
    Join Date
    Jun 2007
    Location
    louisville ky
    Posts
    107
    Post Likes
    Thread Starter
    Quote Originally Posted by beenthere View Post
    Goodman has a listing of temp differences at different CFMs.
    But you need both the outdoor unit and indoor coil model number.
    were would i find the list?

  12. #12
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Goodmans website.
    Click on teh model you have, and download the specs.

  13. #13
    Join Date
    Feb 2008
    Location
    petaluma,ca
    Posts
    53
    Post Likes
    if you return is to loud from being to short. have a company line you return can with acustical insulation, it will reduce the noise by at least 30%.it only takes about a hour or two of labor and the material is cheap

  14. #14
    Join Date
    Jun 2007
    Location
    louisville ky
    Posts
    107
    Post Likes
    Thread Starter
    Quote Originally Posted by furnacemaninc View Post
    if you return is to loud from being to short. have a company line you return can with acustical insulation, it will reduce the noise by at least 30%.it only takes about a hour or two of labor and the material is cheap
    they put what looks like bubble wrap with aluminum foil on both sides of it on the inside of it. the intake is only about 6 inches long

  15. #15
    Join Date
    Mar 2004
    Posts
    60
    Post Likes
    boy i love lack of return air and excessive fpm across filter grill

  16. #16
    Join Date
    Jun 2007
    Location
    louisville ky
    Posts
    107
    Post Likes
    Thread Starter
    Quote Originally Posted by dezerttech View Post
    boy i love lack of return air and excessive fpm across filter grill
    im not a pro but i think i have a lot of return air. i have a 14x25 on the side of the furnace and 4 6inch in the bottom of the furnace. what is fpm

  17. #17
    Join Date
    Apr 2008
    Location
    Princeton, NJ
    Posts
    627
    Post Likes
    Quote Originally Posted by chrism9232 View Post
    what is fpm
    FPM is a measure of velocity...in this case air velocity in feet per minute (speed of air).

    Where CFM is a measure of volume in Cubic feet per minute (amount of air).

    If you know one of these and the square feet of duct area the air is traveling through....you can calculate the other.

    Key1

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •