Thread: charging unit
    charging unit
    I would never charge a system with a dirty coil but have seen an a/c tech charge an orfice type system with 10 seer inside coil, 13 seer outside condenser,and a dirty coil.I guess you could weigh in the additional r-22 but can you be certain the condenser has what it claims to have? Also would this be the same considering the unmatched system? He is doing a superheat but I don't see how that can be done with a dirty coil. I'm always trying to learn and this is an excellent place to do just that.Thanks
    Western NC
    he did it wrong.
    Probably didn't need any refrigerant. Clean the coils and the system woulda worked.
    Now its overcharged and the customer has been a victim of the "gas and go"
    Mis-matched units are tricky, but sometimes that's what you've got. If they're dirty, your chances of getting it right go way down. I make sure they're clean, good air flow, and charge them like a normal system, (SH/SC), but I don't always get perfect results.
    Anyone else have more suggestions for getting a mis-match right? I'll take any ideas.
    Ohio
    Better measure that airflow before you touch that charge also....clean everything then verify airflow...other wise it will never be right.
    I need a new signature.....
    Virginia
    the dirty coil is probably the reason the other compressor failed