    Freon Noise in system

    I have a recently installed Trane XC95 and has been hooked up to my older Lennox A/C unit. They installed a Trane Coil at the furnace when they put in the furnace. My problem: I can hear a loud rush of freon whenever the comprssor starts the A/C cycle. It sound as if I have water hose running at full volume. I never had this sound before. They have checked and adjusted the charge on the freon. I beleive that there is air in the system. When they isntall the A-Coil they forced the freon into the compressor but I don't beleive that the evacuated the system. My concern beside the annoying noise is if air/moiture is in the system will that shorten the life of my compressor? I would like to have the system vacuumed or evacuated and recharged, is the a good solution? As a note there is a TXV on the system and system is cooling fine. Any help would be greatly appreciated.

  2. #2
    Join Date
    Jan 2004
    Location
    PA
    Posts
    75,910
    Post Likes
    Doubt thats the problem.

    The mismatch is more likely the cause.

    The A/C coil is not part of the furnace. Its part of the cooling system, and should be matched to the OD unit.
    Now its not.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  3. #3
    Join Date
    Jul 2008
    Posts
    5
    Post Likes
    Thread Starter
    Beenthere
    thanks for your reply. As as safeguard do you think it advisable to do the evac and recharge anyway? I kinda thought that the two different comp/A coil could be a contributer.

  4. #4
    Join Date
    Jan 2004
    Location
    PA
    Posts
    75,910
    Post Likes
    I doubt it will help.

    If they are willing to try ir, it won't hurt. But more likely then not, you'll still have the noise.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  5. #5
    Join Date
    May 2004
    Location
    Austin, TX
    Posts
    1,829
    Post Likes
    Also check and make sure your smaller copper tubing is not resting against
    the wall. That has been known to amplify the sound.

  6. #6
    Join Date
    Sep 2002
    Location
    I don't know
    Posts
    3,019
    Post Likes
    I wouldn't worry about it provided that the sound is consistent.

    High pressure liquid refrigerant flows to the evaporator and boils off; some systems make more noise than others.

    An intermittent sound would be a cause for concern though.

  7. #7
    Join Date
    Jul 2008
    Posts
    5
    Post Likes
    Thread Starter
    A debt of gratitude to edward301. I found that tube in contact with a few joists and the center beam as well a gas pipe. I wrapped in foam tube pipe insulation and have ran 3-4 cycles and....silence. Just like the old days. Also a sincere thanks to all who responded. Saved enough for at least a tank of gas and a steak!