    Question Blower Speed Question / Lennox VS with IAQ

    http://www.hvac-talk.com/vbb/showthread.php?t=176283

    Had my new system installed Thursday and there are some configuration issues I outlined in the above thread, and a senior tech is coming out Monday to make things right.

    System is Lennox XC16-048 with Lennox G60UHV-60C-090X a five-ton Aspen coil and VisionPro IAQ t-stat.

    My question is should I ask the tech to lower blower speed from its current 2000 CFM (default for furnace) to 1600 CFM given this is a four-ton system (4 X 400 = 1600)?

    At 2000 CFM the new system seems much louder than the old system.

  2. #2
    Join Date
    May 2007
    Location
    DC Metro Area (MD)
    Posts
    3,368
    Unless you're in an arid climate, I'd suggest 400 cfm/ton. 350 cfm/ton if you're in a real humid climate. Also, your ductwork may be a bit undersized for 2000 cfm if 1600 cfm of airflow was what the old system did. Installers should have configured the furnace blower speed properly. 500 cfm/ton is high.

  3. #3
    Join Date
    Jun 2008
    Posts
    20
    Thanks for the reply. This is as I suspected.

    As I mentioned, the installer literally installed the system and turned it on with no configuration of anything. Hopefully we'll get this squared away when tech comes out Monday.