Blower Speed Question / Lennox VS with IAQ
http://www.hvac-talk.com/vbb/showthread.php?t=176283
Had my new system installed Thursday and there are some configuration issues I outlined in the above thread, and a senior tech is coming out Monday to make things right.
System is Lennox XC16-048 with Lennox G60UHV-60C-090X a five-ton Aspen coil and VisionPro IAQ t-stat.
My question is should I ask the tech to lower blower speed from its current 2000 CFM (default for furnace) to 1600 CFM given this is a four-ton system (4 X 400 = 1600)?
At 2000 CFM the new system seems much louder than the old system.
-
07-12-2008, 03:04 PM #2
Professional Member*
- Join Date
- May 2007
- Location
- DC Metro area
- Posts
- 3,234
Unless you're in an arid climate, I'd suggest 400 cfm/ton. 350 cfm/ton if you're in a real humid climate. Also, your ductwork may be a bit undersized for 2000 cfm if 1600 cfm of airflow was what the old system did. Installers should have configured the furnace blower speed properly. 500 cfm/ton is high.
-
07-12-2008, 03:18 PM #3
Regular Guest
- Join Date
- Jun 2008
- Posts
- 20
Thanks for the reply. This is as I suspected.
As I mentioned, the installer literally installed the system and turned it on with no configuration of anything. Hopefully we'll get this squared away when tech comes out Monday.