    Stumped!

    Help!! 2.5 Ton Goodman Heat Pump, when unit first turns on in cool, the suction psi is between 35-45psi, head pressure is between 125-150psi. These pressures hold steady at those psi's for 15-25 mins then both pressures slowly start rising and steady off at 70-75 low and 250-270 high depending on conditions. Problem is if pressures do not start rising fast enough sometimes unit will start freezing at evaporator. Unit does not freeze all the time just sometimes very infrequent. The air filter is clean, evaporator is clean, condensor is clean and evap. fan is running good on high speed. Could I have a restriction at the orifice, but usually the circumstances are the reverse of what i am finding. Any thoughts would be appreciated. The compressor was replaced in April 08 and has been running good up until about a week ago.

  2. #2
    Join Date
    Dec 2007
    Location
    Kansas
    Posts
    80
    Are you sure the indoor fan is coming on when pressure reagings are low?

  3. #3
    Yeah, indoor fan comes on every time.

  4. #4
    Join Date
    Dec 2007
    Location
    Ohio
    Posts
    2,876
    Superheat?
    Subcooling?

    Just because your fan in on high doesn't mean it's right. Have you tested staic pressure to determine CFM?

    Sounds like a charge issue to me but without more information, hard to tell.
    I need a new signature.....

  5. #5
    How do you test staic pressure?

  6. #6
    Join Date
    Dec 2007
    Location
    Ohio
    Posts
    2,876
    Jog.....don't take this the wrong way but if you have to ask, you may need to call a service professional out to evaluate your system. If you are a professional, get your post count up to 15 and apply for professional status on this site. There is a wealth of information on here, including step by step procedures for testing static pressure.

    We are not allowed to give out DIY advise on the open forums of this site but once you are professional, we can talk shop all day and night.

    I can tell you this....we test static pressure to get the amount of CFM a blower is moving. If you follow the 400 CFM per ton rule then your indoor blower should be moving as close to 1000cfm as you can get. After that is verified, then you can begin adjusting your refrigerant charge using superheat and subcooling measurements.
    I need a new signature.....

  7. #7
    O.K. thanks for the heads up. I am not a pro. just a maintenance tech at a n apartment complex, only been in the hvac/maintenace field about a year so this is really the first unit i have had that has given me a problem I couldnt figure out and my superiors think it is a bad compressor but i am not sure and dont want to just changing out parts if you no what i mean!

  8. #8
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,928
    Was it the compressor that was changed out in April, or the condenser.

    What are the chances that someone has added gas to get the vapor pressure up.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  9. #9
    Join Date
    Jan 2005
    Location
    USA
    Posts
    1,450
    Quote Originally Posted by Jogalloway View Post
    O.K. thanks for the heads up. I am not a pro. just a maintenance tech at a n apartment complex, only been in the hvac/maintenace field about a year so this is really the first unit i have had that has given me a problem I couldnt figure out and my superiors think it is a bad compressor but i am not sure and dont want to just changing out parts if you no what i mean!
    Still get your post count up and apply for pro status if you get it you will get all kinds of really good info from all of these great techs. Being a rookie does not mean that you are not a pro, it is defined by the way you approach problems and asking questions before making mistakes is the first step in the pro-direction. Good Luck
    "It's always controls"

  10. #10
    Join Date
    Jun 2008
    Location
    Morgantown, WV
    Posts
    129
    You either have an air flow issue or a leak that needs to be repaired, assuming an R22 system.

    Best thing to do is to get a good evaluation from a reputable company and pay them to fix the problem. Easy as pie. Find a company tha guarantees their work the first time and let them figure it out.

  11. #11
    Join Date
    Jan 2005
    Location
    USA
    Posts
    1,450

    Thumbs down

    Quote Originally Posted by diverdan View Post
    You either have an air flow issue or a leak that needs to be repaired, assuming an R22 system.

    Best thing to do is to get a good evaluation from a reputable company and pay them to fix the problem. Easy as pie. Find a company tha guarantees their work the first time and let them figure it out.
    It is amazing that you are able to diagnose that with so little information. Uh hire a company to do your job for you, brilliant why did I not think of that. You need to be careful not to lead a person in the wrong direction, it can be very costly to both the customer and the contractor. Not trying to be mean but try to get all of the info before you take blind stabs at the problem, it is kind of like defrosting a freezer with an ice pick.
    "It's always controls"

  12. #12
    Join Date
    Jun 2008
    Location
    Morgantown, WV
    Posts
    129
    Your criticism of my diagnosis reflects an unsound technical background.

  13. #13
    Join Date
    Dec 2003
    Location
    Citrus County, Florida
    Posts
    1,521
    if it's a TXV system, could be a plugged equalizer.
    Doug

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event