  1. #1
    Join Date
    Jul 2008
    Posts
    6
    Post Likes

    Unhappy Wife's Running Out of Patience

    Help! My 12 yr old Carrier unit had a compressor burnout a couple of weeks ago and I'm trying to decide what to do. The cost to repair the existing unit is not cheap so I'm leaning towards replacing both the outdoor unit and the airhandler (which isn't cheap either but it's all relative I guess). I had 4 companies give me qoutes on varies brands and price levels within each band (13-17 SEER, variable speed versus single, 2 stage compressor versus single, etc). Quoted sizes ranged from 3-4 tons. Some of the companies pointed out issues with my existing duct work, some didn't mention it at all. After digesting the various quotes, I think I've settled on one of the companies to do the work based on what I perceive to be the most thorough job of evaluation. There are still 2 areas I'd like help with. 1) The company I've selected is insisting a 4 ton unit is needed based on their calculations but it seems on the high side to me and 2) they've offered 3 options, 2 based on Carrier equipment and 1 based on Lennox (they also carry Trane) and I'm not sure which one to pick.

    Info on current system: 1996 date code
    Carrier 3.5 ton (38YCB042300)
    Carrier 4.0 ton airhandler (p/n FC4BNF048000AEAA)

    House Info:
    Total sq ft = 3200
    Location: Orlando Fl, east west orientation with lots of single pane glass
    This A/C unit services approx 1260 sq ft of the total house and includes kitchen, dining room and large great room with high cathedral ceiling. Current return is too small for the existing 3.5 Ton unit and located in the kitchen. The estimator recommend almost doubling the size and moving it 2/3 up the great room to pull the hot air out of the cathedral ceiling area.

    Options:

    1) 4 ton Carrier Infinity 16 (25HNA648A) with variable speed airhandler (FE4ANB005)

    2) 4 ton Carrier Comfort B (25HCA348A) with variable speed airhandler (FV4BNF005)

    3) 4 ton Lennox (XD-19-048) with variable speed airhandler (CBX32MV-048)

    Both the Infinity and Lennox have a large rebate which makes them very close in cost to the Carrier Comfort B. The Lennox 17 SEER and Carrier Infinity 15.8SEER quoted costs are virtually the same so which is the better value when considering the differences in efficiency and quality / reliability of each brand?

    Any advice is greatly appreciated since the wife is over my analysis paralysis!!

  2. #2
    Join Date
    May 2007
    Location
    DC Metro Area (MD)
    Posts
    3,402
    Post Likes
    4 tons for 1260 sq. ft.?

    I see that you are in Florida with lots of glass, but 4 tons still sounds like a lot. Only a load calculation will tell. I can tell you that for my house, which has around 3500 sq. ft. of conditioned living space, 3.5 tons does just very well cooling and dehumidifying. I do have shade, though, and I'm not in Florida. Just trying to give you an idea.

    If they did a load calculation, ask to see the results in writing. Looking at ductwork and making proper modifications is important. It looks like this company plans to make some changes for improved performance out of the system. For a 4-ton system, I'd recommend more than 1 return, but that's my opinion.

    With your climate, I think the Carrier Infinity or Lennox Signature Series systems would be the better choices. What thermostat is included with the Lennox? The 60% capacity of the Infinity 16 on low stage makes it an attractive choice for your climate and potential oversize.

  3. #3
    Join Date
    Jul 2008
    Posts
    6
    Post Likes
    Thread Starter
    Ryan - thanks for the response. I'm somewhat concerned anout the size as well since the current unit is 3.5 tons but the company measured all the windows, sq footage, went up in the attic, noted orientation of house and effect of of the great room cathedral ceiling which peeks around 20 ft. The kitchen and dining room are 8 ft ceilings but everything is essentially one big room. I haven't asked to see the actual calc's. Two of the companies (including the one I think I'm going with) noted the current single return is sized for a 2 ton unit. I don't know if they intend to add another return high up in the great room and keep the existing return in kitchen or simply replace the one in the kitchen with a single return in the great room - I'll ask.

    Thermostat for the Lennox option was a 7000 digital / programmable.

    Thanks again.

  4. #4
    Join Date
    Jun 2008
    Location
    Las Vegas, NV
    Posts
    224
    Post Likes
    Down the road be aware that repair costs on a Carrier are probably going to be higher than on a Lennox.

    Barrie

  5. #5
    Join Date
    Dec 2002
    Location
    Houston,Texas
    Posts
    23,010
    Post Likes
    Quote Originally Posted by barriehie View Post
    Down the road be aware that repair costs on a Carrier are probably going to be higher than on a Lennox.

    Barrie
    Now how on earth do you figure that?
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards" ~ Vernon Law

    "It's what you learn after you know it all that counts." ~ John Wooden

    "When the teachers become unteachable we're all in trouble" ~ Mr. Bill

    "Remember "Pro" is only a name, it's not always a mindset determined to do everything correctly" ~ Mr. Bill




  6. #6
    Join Date
    Mar 2008
    Posts
    206
    Post Likes

    Eh ?

    Quote Originally Posted by barriehie View Post
    Down the road be aware that repair costs on a Carrier are probably going to be higher than on a Lennox.

    Barrie
    You are Carrier dealer or installer give him a heads up right?

  7. #7
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,835
    Post Likes
    jcurry,

    3.5 sound high,how did the old system do,run a lot on hot days ,or not?


    What tonnage is the other system?

    Did they measure the peak of the cathedral?

  8. #8
    Join Date
    Apr 2008
    Location
    TEXAS
    Posts
    1,706
    Post Likes
    Quote Originally Posted by barriehie View Post
    Down the road be aware that repair costs on a Carrier are probably going to be higher than on a Lennox.

    Barrie
    they must have a lennox parts house on every corner in las vegas!
    "When the people find they can vote themselves money,that will herald the end of the republic" - Benjamin Franklin

    "Government is not reason, it is not eloquence, it is force;like fire, a troublesome servant and a fearful master. Never for a moment should it be left to irresponsible action"- George Washington

  9. #9
    Join Date
    Jul 2001
    Location
    Fairfield and NewHaven Counties in Commecticut
    Posts
    4,982
    Post Likes
    Quote Originally Posted by smittyii View Post
    they must have a lennox parts house on every corner in las vegas!

    [/I]

    cant buy lennox parts in Ct
    Quality and Value Service and Repair

  10. #10
    Join Date
    Jul 2008
    Location
    Oviedo, Florida
    Posts
    2
    Post Likes
    JcurryFL,

    I feel your pain. As I live in lovely Central Florida also. I have a pair of older (about 10 years old) Carrier units (SEER 10's). Since my home is a split level they did two units 2.5 ton for upstairs (700 sqft) and 3.5 ton for downstairs (1700 sqft). In our area, they tend to oversize to compensate for the near 100% humidity during the summer that really lowers the heat exchange between the air and the heat pump. But I would recommend that if you are still worried about the oversizing, then ask more questions.

    Jim

  11. #11
    Join Date
    May 2007
    Location
    DC Metro Area (MD)
    Posts
    3,402
    Post Likes
    Quote Originally Posted by jims2321 View Post
    JcurryFL,

    I feel your pain. As I live in lovely Central Florida also. I have a pair of older (about 10 years old) Carrier units (SEER 10's). Since my home is a split level they did two units 2.5 ton for upstairs (700 sqft) and 3.5 ton for downstairs (1700 sqft). In our area, they tend to oversize to compensate for the near 100% humidity during the summer that really lowers the heat exchange between the air and the heat pump. But I would recommend that if you are still worried about the oversizing, then ask more questions.

    Jim
    Oversizing is actually worse for humidity control. The shorter cycles satisfy the thermostat's setpoint before being able to remove enough humidity (latent heat). There are, however, thermostats that are better at controlling humidity and actually have humidity setpoints. Longer run cycles help with humidity removal, and that's where a properly-sized dual-stage unit really helps (running in low stage). That's not to say a properly-sized single-stage unit can't provide adequate humidity control.

  12. #12
    Join Date
    Apr 2008
    Location
    TEXAS
    Posts
    1,706
    Post Likes

    Confused

    i can't see the need for a 4 ton, but maybe the contractor knows something we don't. i also don't see why u need to remove the heat from a cathedral ceiling. does someone have a hammock strung across it for sleeping? high ceilings are dead space unless they have windows (heat gain) in fla. you want living space conditioned.
    "When the people find they can vote themselves money,that will herald the end of the republic" - Benjamin Franklin

    "Government is not reason, it is not eloquence, it is force;like fire, a troublesome servant and a fearful master. Never for a moment should it be left to irresponsible action"- George Washington

  13. #13
    Join Date
    Jul 2008
    Posts
    6
    Post Likes
    Thread Starter
    Thanks for everyone's inputs. Sounds like I need to have the company run through the load calc's and convince me that 4 tons is the right answer. If I went with the 4 ton Infinity 16 with the 2 - stage compressor, would the unit spend most of the time effectively running as ~ 2 ton unit with the 2nd stage available for peak summer heat loads? Would the Lennox XP-19 operate the same? Still not sure which config is right for my situation.

  14. #14
    Join Date
    May 2007
    Location
    DC Metro Area (MD)
    Posts
    3,402
    Post Likes
    Quote Originally Posted by jcurryfl View Post
    Thanks for everyone's inputs. Sounds like I need to have the company run through the load calc's and convince me that 4 tons is the right answer. If I went with the 4 ton Infinity 16 with the 2 - stage compressor, would the unit spend most of the time effectively running as ~ 2 ton unit with the 2nd stage available for peak summer heat loads? Would the Lennox XP-19 operate the same? Still not sure which config is right for my situation.
    If the unit is properly sized, it should spend a good amount of time in low stage. The XP19 will have more capacity in low stage with the scroll compressor. I just recently learned from someone here that to dehumidify, the ComfortSense 7000 will keep the blower on low and bump the unit outside to high stage to provide more dehumidification. Essentially, they're both good systems. You'll have to weigh all the features and benefits that each has to offer.

  15. #15
    Join Date
    Aug 2004
    Location
    Florida, Kentucky, Michigan, Ohio, Arizona, Colorado, Nevada, and Califormia
    Posts
    410
    Post Likes
    Everyone has taken all of the good technical replies..so my thunder is gone. All good advice. I'd try to relocate the return in the kitchen though. Kitchens and bathrooms are no places for returns. If your wife cooks like mine, when dinner is burned evey day @7pm, the return let's us enjoy blackened food, with a side of smoke all through the air handler and every room in the house. No return in the bathroom for the same eye burning reasons.
    "Surprised ?! If I woke up tomorrow with my head sewn to the carpet, I wouldn't be more surprised."
    Clark Griswold

  16. #16
    Join Date
    Jul 2008
    Posts
    6
    Post Likes
    Thread Starter
    Ira - You're dead on with the dinner comment even though my wife's a great cook (maybe she'll read this and I'll get lucky tonight, or killed. LOL) I don't like smelling pork chops in half the house all night. I'm leaning towards the Lennox based mostly on Ryan's comments which seem to make sense even though the Carrier will probably work just as well. Thanks all.

    Go Big Blue!!

  17. #17
    Join Date
    May 2007
    Location
    DC Metro Area (MD)
    Posts
    3,402
    Post Likes
    The Carrier on low will have longer run times with less capacity, so it should remove humidity well, too.

    I'm just going by what M Kilgore said, "The Comfortsence will bump up the unit to high stage and leave the blower on low stage on a call for dehumidification. This removes more humidity. The IAQ uses low speed compressor and fan."

    I don't think you can go wrong with either one. Lennox and Carrier make good equipment. I like the scroll compressor of the Lennox that allows the unit to switch stages on the fly, whereas the reciprocating compressor has to STOP to switch stages. Starting and stopping a compressor vs. switching on the fly, I'd choose the latter, though I wish the scroll had a lower net capacity on low stage. Carrier's Infinity 19 uses a scroll compressor, but it costs more.

    Lennox combo: 17.00 SEER, 9.00 HSPF, 12.35 EER
    Carrier combo: 15.80 SEER, 9.10 HSPF, 11.60 HSPF

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •