This is not a DIY site, but I can tell you that when you add more load to a system, that system works harder.
Check for insulation problems on the ducting that runs through unconditioned areas. Check you air filter. That's about it for HO testing.
I am wondering if my unit is doing all that it can do. After we added on to the house, it seems like its more difficult for the house to cool off. The unit is a Armstrong 3-ton about 12 years old. Today, I done a little checking. It was 84 degrees outside. The humidity was probably about 60%. I measured the temp at the register that was the most distance from the unit and it was 64 degrees with 90% humidity. The air at the closest register was the same. The air at the return was 73 degrees at 60% humidity. That's only a 9 degree difference. Also, is there a simple way to check to see if my air flow is sufficient. Any ideas would certainly be appreciated.
This is not a DIY site, but I can tell you that when you add more load to a system, that system works harder.
Check for insulation problems on the ducting that runs through unconditioned areas. Check you air filter. That's about it for HO testing.
Training is important!
Practical Training is a must!
Measuring temps at the registers seldom tells you anything.
Have a service tech check it.
Sounds like you added on, and robbed your other supply's for air.Big no,no Your system was'nt designed to handle the addition. 12 years ago, yeah today ,no. Sorry man you need a bigger system.
Who done your duct work to your addition?
The original duct is insulated metal duct, but the extension from the original placement of the unit to where it is now is flexible insulated tubing. The house is 2-story with a separate system for the upper floor. The bottom story sq footage is about 1600sq ft., but a lot of the spaze is open except for the great room which has 18ft cathedral ceilings with the ceiling fans. I would have thought that a 3-ton unit would have been sufficent, but my air flow doesn't seem all that great.
was the system running the duringthe remodel
What did Manual J call for after renovations?
The original installer was also the one who done the upgrade. He thought the unit was sized enough with the additional 480sq. ft. addon. I'm not sure if I want to go to the expense of putting in a new system when we may not even be living here in the next 2 or 3 years. I heard that a new regulation was going into effect in 2009 and was told it would be better to wait until then if I decided to replace it. Not sure what the new regulation was though.
They probably ment 2010, for No new units being made using Virgin R22.
You can get a new unit today using teh R410A refrigerant, you don't have to wait.