    Just curious if I should do anything or just leave the system alone.
    I have a 3-ton Carrier 13 SEER AC unit installed about 5 years ago. The house is 1,100 square foot ranch home (small). I have re-insulated the attic since installing the AC. The AC is combined with my Oil-fired Carrier 84K BTU furnace. The house is in New York State. Lower end of the state.
    I haven't done any load calculations, but I have to imagine that 3 tons is way too much for the home and I am paying much more electric costs than I need.
    Is it economical to switch the AC to a smaller size? Are there more things involved than simply switching the outside unit?
    The furnace is fine, i only use about 350 gallons of fuel oil in a typical winter and the house is comfortable at 67 degrees, so I wouldn't want to replace it.
    The AC is comfortable, but it doesn't remove humdidity as well as it should and I always feel like I am paying for this huge AC unit to run when I may just need a tiny one. But I don't want to switch it out if it will take 10 years to recover the cost or something like that. I only want to switch it out if it is a "no-brainer".
    Duct work in the house consists of one major rectangular duct and then individual 5-inch metal ducts feeding the individual registers. The air for both the heat and ac comes out of the ducts very rapidly. I have one return vent located in a back hallway about 1.25 ft by 2.25 ft (haven't measured it).
    The fan is noisy and also the sound of the air going through the vent is pretty noisy. I have learned to live with the noise however. It is really the energy usage that I am concerned I am using way more electricity than I need to be.
    any thoughts?
    You need a Pro that can test the static(air flow resistance),and adjust the fan speed ,so you are at 350 cfms per ton,to increase dehumidification.
    I have an anometer (measures air velocity in FPM) at work that I have access to. Can I simply make a rough estimate myself by determining the flow rate in CFM at each individual register and adding them together? Then I can get back to you with what I measure to see if I'm way over or at about the 1,050 CFM that I should be at?
    He may already be at 350 per ton.
    Have it checked. if its already at 350 or less. You may want to consider having the A/C replaced with a properly sized HP, so you have a hybird/dual fuel system.
    Tht could easily drop another 100 gallons off your oil consumption. And repay you for the replcaement cost in a relatively quick time.
    Unless oil is cheaper in NY, then it is in PA.
    I am hardly using any oil right now (350 gallons). People with larger homes are using upwards of 800 to 1000 gallons, so I am not as concerned with the fuel oil usages as I am with the oversized AC.
    Probably won't be that accurate,and if you lower the cfms too much ,you can damage the the equipment,i.e. Compressor.
    It also won't show any air the is lost thru supply duct leakage,and you need 350 cfm per ton across the coil.
    Since it appears to be oversized,this may not help as much as is needed.
    Jun 2007
    The Twilight Zone
    Quote Originally Posted by brewyourown View Post
    350 gallons x $4/gallon = $1400
    What was oil last year? $2.50/gallon?
    350 x 2.5 = $875. This winter you'll spend an extra $525 if the temps are similar to last winter.
    Good luck.
    I understand that.
    And $1,400.00 at 4 bucks a gallon for heat isn't bad.
    But a new A/C may or may not save enough to show a return in a reasonable amount of time.
    A dual fuel heat pump will offset most of the cost of a new unit in heating saving. And still leaves you with the warmer air temp of your oil furnace when its cold ouside.
    And if oil hits 5 bucks a gallon this winter. The ROI is much quicker yet.
    I understand that.
    I understand now. I had always been told that Heat Pumps were much more expensive and have never even considered them. Where can I find out more about them? Would this heat pump provide air conditioning as well? sorry for being naive, but hopefully this forum can benefit people like me.
    Your local contrators should be able to tell you what you need to know.
    Oil companies have little to NO incentive to want you to get a HP add on to your furnace. So they are seldom the best place to go.
    Your oil furnace will remain. You'll get a new indoor coil.(it will look pretty much like what you have now)
    A new outdoor unit(the heat pump)
    And a dual fuel control.(Many new thermostats are dual fuel controls)
    It can be set to lock out the heat pump at any outdoor temp. The common temps are 40 to 20.
    Many use 40° outdoor temp to prevent the heat pump from going into defrost. And to prevent the discharge air temp from getting to cool.
    I find many people are still satisfied with the discharge air temp at 35° outdoor temp. And it saves alot more on oil at 35 then 40, If the heat pump can handle the heat load at that temp.
    Jun 2007
    The Twilight Zone
    Read the post on "Hallowell Acadia - where does it become practical". The post is on this page near your post. I compared the cost of oil heat with that of a heat pump.
    Take care.
    How much will a 15/16 SEER HP save over a 13 SEER HP ?
    And yes; I realize that heat pumps are rated differently - but the HP efficiency follows the AC efficiency too - right? <g>
    In terms of heating - how much less will the highest efficiency HP system cost to operate versus the lowest efficiency HP system?
    PHM
    QUOTE=beenthere;1921049] . . . . A dual fuel heat pump will offset most of the cost of a new unit in heating saving . . . . .
    QUOTE]
    PHM
    PHM
    QUOTE]
    I believe you are interpeting my recommendation to use a HP.
    I never said to get a super high efficiency HP.
    He has a 13 SEER A/C, using his current oil furnace. Installing a 15 SEER single stage A/C on it, won't pay back over the course of the A/Cs life span.
    But a 13 to 15 SEER single stage heat pump will.
    A higher SEER will save some in cooling, but only a little more in heating.
    A 15 SEER heat pump 2 ton, may have a 14,800 BTU output at 17 OD temp, and a 13 SEER may have a 13,100 BTU output at same outdoor temp.( Those are actual York unit ratings, not made up)
    An 11.5% difference in heat output.
    On a dual fuel, that can change the balance point from 35 for the 13, to 30 for the 15.
    Or, a couple degrees warmer air discharge temp. at the higher OD temps.