    New AC not so cool

    Yesterday we had our 22 year old 3 ton York heat pump replaced with an Amana ASX14 1.5 ton (Our house is only 1500 sqft). The new unit us much quieter and will save us allot of $$ on electricity but it seems to cool way less than the old York it replaced.

    I recall reading somewhere that the unit comes pre-charged (R410) for 15ft of tubing but the distance from my condenser to coil is easily over 30ft.

    Could this be the reason why the units cooling performance is so poor?

    Thanks!

    (The installer ran the vacuum discharge for about an hour before turning the unit on, was this enough to get air out of the system?)

  2. #2
    Join Date
    May 2007
    Location
    DC Metro Area (MD)
    Posts
    3,371
    The installers should have adjusted and checked the refrigerant charge.

    The system may be undersized. The nominal capacity of the system was cut in half. Was a load calculation done to warrant this change in capacity?

  3. #3
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,759
    Your 3 ton may have been over sized.
    How did they determine that your house only needs 1.5 tons.
    Did they do a load calc, or did they just guess, based on 20 to 30 years of guessing.

    Yes, a low charge does cause poor cooling.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  4. #4
    Thanks for the quick reply!

    I don't think the installer checked the charge post installation, that's my worry.

    A load calculation was done during the energy audit and the old 3-ton was deemed over sized for our small house.

    I will call back the installer and have him check the charge.

  5. #5
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,759
    What area are you in. And what did the load calc say the load was.

    Although not impossible for 1.5 ton to be the right size for a 1500 sq ft home.(1000 sq ft per ton)
    If its a rancher, few of them get by with only 1.5 tons.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  6. #6
    Sorry, I do not have the load calc info with me here at work. We are just outside of Toronto Canada.

  7. #7
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,759
    After they check the charge. If its still performing poorly. I would suspect a sizing error.
    I would ask to see the load calc nmbers.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  8. #8
    Join Date
    Jun 2005
    Location
    SW Wisconsin
    Posts
    5,031
    Toronto, Canada summer design 87 dry bulb 72 wet bulb 48 to 49 %RH.

    A high humidity level in your home will affect the cooling performance.

    At this point, I would NOT condemn the sizing of the equipment.
    There could be a lot of things wrong with the setup of the system!


    I hope the airflow CFM is correct for the 1.5-ton system.
    Have the duct system checked for hot Return Air leaks.

    Should have added the correct amount of R410, - perhaps not!
    IMO, in Toronto, with the proper reductions in heat gain, & correct airflow CFM, a properly functioning 1.5-ton should be enabled to work okay.

  9. #9
    Thanks everyone!

    I spoke to the installer and he is coming to check out the performance this weekend.

  10. #10
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,759
    Cool.

    Have him check it by Amana's sheets.
    They have a good spec sheet for how your unit should be performing.

    As Udarrel said, 13,500 BTUs of sensible may be enough.
    Then again, it may not.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  11. #11
    Join Date
    Jun 2005
    Location
    SW Wisconsin
    Posts
    5,031
    Quote Originally Posted by TheDogFather View Post
    Thanks everyone!

    I spoke to the installer and he is coming to check out the performance this weekend.
    Copy only the data portions & paste in your Word-Processor, make a couple hard-copies, then get as much of this data as the tech will provide for you.

    TROUBLE SHOOTING DATA
    TXV or orifice metering device? _______

    Outdoor condenser’s DB discharge-air-temperature _____
    Out-Door temperature: ____
    Condenser air split _____

    Indoor Total-ESP _______
    All Supply Air velocities in FPM: ___
    I'll figure the total CFM:


    Suction line pres. _____
    Suction-Vapor line temperature: _______
    SST – Gage - Suction Saturated Temperature. ______
    Superheat ______

    Head pres. _______
    SCT – Gage - Saturated Condensing Temp _______
    Liquid line temperature: _______
    Subcooling: _______
    Return Air temp DB &, WB or %RH: _______
    Supply Air temp DB &, WB or %RH: _______

    With the information data below and an accurate CFM airflow + sea-level height, I can ball-park its BTUH output
    Return Air temp DB &, WB or %RH: __
    Supply Air temp DB &, WB or %RH: __

    Except for the pressures you can take most of the readings for us.

    My advice: get a low cost humidity gage at a local hardware store & see what the percentage-RH is in your home, I can cross-reference that to the wet bulb depression.

    Then, perhaps we can provide a ballpark BTUH & an opinion on how well the 1.5-ton system is performing. - Darrell

  12. #12
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    68,974
    Quote Originally Posted by udarrell View Post
    Toronto, Canada summer design 87 dry bulb 72 wet bulb 48 to 49 %RH.

    A high humidity level in your home will affect the cooling performance.

    At this point, I would NOT condemn the sizing of the equipment.
    There could be a lot of things wrong with the setup of the system!

    I hope the airflow CFM is correct for the 1.5-ton system.
    Have the duct system checked for hot Return Air leaks.

    Should have added the correct amount of R410, - perhaps not!
    IMO, in Toronto, with the proper reductions in heat gain, & correct airflow CFM, a properly functioning 1.5-ton should be enabled to work okay.
    All good points. What indoor equipment was installed? How was the blower set up?
    Government is a disease...
    ...masquerading as its own cure…
    Ecclesiastes 10:2 NIV


Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event