Thread: Is 0.5 max static pressure a realistic target?

  1. #21
    Join Date
    Apr 2008
    Location
    Princeton, NJ
    Posts
    627
    Post Likes
    Thread Starter
    Quote Originally Posted by beenthere View Post
    Don't forget to install balancing dampers.
    I won't ...

    Thanks for all of the help....

    I will post again after stage 1 is complete with a SP update.

    Key1

  2. #22
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,835
    Post Likes
    Quote Originally Posted by key1cc View Post
    Well the work has already started and it is divided into three stages.
    Stage 1 is to add the new 14x14 trunk which transitions to a 16x 12 then a 16x8 before linking up with seven 5" round runs which will be converted to 6" rounds. After that is done The static and air flow will be assessed then....
    Stage 2 will be considered which will widen the 8x9.5 trunk to 16x8 and all five of the 5" round runs will be converted to 6" round.
    Stage 3 will be to convert the 24x10 return drop into a 24x16 return drop with a 5" media filter cabinet.

    Hopefully all of that will get me down to my realistic target of 0.7 or less.

    Key1
    did you view the sketch I posted?

    from the pics in the other thread,a lot could have been done to improve the take-offs from the plenum and on the return as well.

    Increasing the size isn't the only way to reduce the static.

    Adding a 5" filter to the side of the furnace,isn't the best way to do it.

    Wondering if the furnace is large enough to requie,bottom or returns from both sides,might want to check on that.

  3. #23
    Join Date
    Aug 2006
    Location
    Dallas (Plano), TX
    Posts
    168
    Post Likes
    Quote Originally Posted by key1cc View Post
    ... Stage 3 will be to convert the 24x10 return ... into a 24x16 return ...
    I'm surprised this is step 3, and instead not an earlier step.

    Doesn't changing the return from 24x10 to 24x16 change the return cfm capacity from about 1050 to about 1600 cfm (assuming 700 fps)?

    And since the unit is 4 ton, would the aproximate max cfm capacity be 1600, assuming 400 cfm/ton?

    Thus, simply to have the return sized to the capacity of the 4 ton unit, shouldn't the return be at least 24x16?

    Thanks and best regards,

    Bill

  4. #24
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    His return is more restrivtive then his supply.
    So increasing the return first would increase his upply static and possibly make a noise problem.

    The 16 x 24 return will allow him to get get a longer life from his media filter before the pd across it becomes too much.

    When he puts his factory filter in, his supply static goes from .55" to .62", so his supply needs attention.

  5. #25
    Join Date
    Aug 2006
    Location
    Dallas (Plano), TX
    Posts
    168
    Post Likes
    beenthere, thank you.

    Interesting.

    Sound like in fact, both the supply and return sides need to be fixed to really have an optimized system that runs with maximum efficiency.

    Best regards,

    Bill

  6. #26
    Join Date
    Jun 2005
    Location
    SW Wisconsin
    Posts
    6,627
    Post Likes
    Quote Originally Posted by dash View Post
    It would help,but can't say how much,or how it will effect the room by room air flow and resulting temperatures.If we were on site and tested,we could predict the performance,can't tell from here.

    Pictures of the supply plenum and trunk take-offs could tell a lot.Often these can be improved to reduce the static.

    Here's a sketch of a furnace,coil and plenum,showing how adding vanes or an angled take-off can reduce the static.This was for another thread ,a while back.In your case you'd want to improve all the trunk take-offs ,not just one.
    Liked your drawing, the turning vanes & extra area at the duct take-offs make a huge difference!

    Well, I would design a heat pump duct system at 450-cfm per/ton or 1800-cfm.

    It is not easy to design for 1800-cfm & above on residential systems.
    You should try for the 0.5" ESP, at least at a 350-cfm per/ton you might achieve the 0.5" ESP. ESP is after the filter & before the blower & before the evaporator coil.

    For the ESP, I would want it before the condenser coil on a high efficiency condensing furnace, otherwise it won't yield the full ESP. There ought to also be predrilled capped holes to check the drop across the HE furnace condensing coil.
    http://www.udarrell.com/proper_cfm_b...g_systems.html - Darrell

  7. #27
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    You would want what before the secondary HX?

  8. #28
    Join Date
    Apr 2008
    Location
    Princeton, NJ
    Posts
    627
    Post Likes
    Thread Starter
    Quote Originally Posted by dash View Post
    did you view the sketch I posted?

    from the pics in the other thread,a lot could have been done to improve the take-offs from the plenum and on the return as well.

    Increasing the size isn't the only way to reduce the static.

    Adding a 5" filter to the side of the furnace,isn't the best way to do it.

    Wondering if the furnace is large enough to requie,bottom or returns from both sides,might want to check on that.
    I saw your sketch but stage 1 of the duct work has already started. I will consider it for stage 2. Increasing the take-off from 8x9.5 to 8x16 is a lot easier and cheaper than increasing the entire trunk duct.

    What do you mean returns from both sides?? This is the 1st time I've heard of this. Would'nt I have to run an entire new length of return duct and add a return grille somewhere in the house to connect it to? Or are you suggesting to tie it in to the existing panned return duct in the basement (which covers 2 joist bays before branching out to the 5 return grills in the house?)
    Key1

  9. #29
    Join Date
    Apr 2008
    Location
    Princeton, NJ
    Posts
    627
    Post Likes
    Thread Starter
    Quote Originally Posted by a0128958 View Post
    I'm surprised this is step 3, and instead not an earlier step.

    Doesn't changing the return from 24x10 to 24x16 change the return cfm capacity from about 1050 to about 1600 cfm (assuming 700 fps)?

    And since the unit is 4 ton, would the aproximate max cfm capacity be 1600, assuming 400 cfm/ton?

    Thus, simply to have the return sized to the capacity of the 4 ton unit, shouldn't the return be at least 24x16?

    Thanks and best regards,

    Bill
    I agree the return is too small, but with a static of 1.1 and 0.8 coming from the supply....I took Beenthere's advice and adressed that first.

    Key1

  10. #30
    Join Date
    Apr 2008
    Location
    Princeton, NJ
    Posts
    627
    Post Likes
    Thread Starter
    Quote Originally Posted by udarrell View Post
    It is not easy to design for 1800-cfm & above on residential systems.
    You should try for the 0.5" ESP, at least at a 350-cfm per/ton you might achieve the 0.5" ESP. ESP is after the filter & before the blower & before the evaporator coil.
    - Darrell
    My dips are currently set for 350 cfm/ton.....and I have 1.1 total SP.

    Great web-site by the way. I have referenced it many times.

    Key1

  11. #31
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,835
    Post Likes
    Quote Originally Posted by key1cc View Post
    I saw your sketch but stage 1 of the duct work has already started. I will consider it for stage 2. Increasing the take-off from 8x9.5 to 8x16 is a lot easier and cheaper than increasing the entire trunk duct.

    What do you mean returns from both sides?? This is the 1st time I've heard of this. Would'nt I have to run an entire new length of return duct and add a return grille somewhere in the house to connect it to? Or are you suggesting to tie it in to the existing panned return duct in the basement (which covers 2 joist bays before branching out to the 5 return grills in the house?)
    Key1
    Larger furnaces require this for proper airflow/static.Check the install manual.

  12. #32
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Don't recall seeing a requirement for both sides for a 4 ton system on any furnace.

    5 tons, as far as I know they all do.

  13. #33
    Join Date
    Apr 2008
    Location
    Princeton, NJ
    Posts
    627
    Post Likes
    Thread Starter
    Quote Originally Posted by dash View Post
    Larger furnaces require this for proper airflow/static.Check the install manual.
    I have read my Trane installation manual cover to cover and it mentions nothing about this. In fact the only time the words "return air" comes up is for instructions of how to install the filter rack on the bottom or on the side.

    The manual is written fo all sizes of direct vent 2-stage condensing furnaces with variable speed....and for AC's from 1.5 to 5 ton. It never mentions duct sizing or return sizing or whether there should be multiple returns sites.

    It does however tell you the static pressure range versus CFM and wattage.

    Key1

  14. #34
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,835
    Post Likes
    Quote Originally Posted by beenthere View Post
    Don't recall seeing a requirement for both sides for a 4 ton system on any furnace.

    5 tons, as far as I know they all do.
    It was just a question,agree 4 tons is not an issueusually around 1800 cms.How large is the furnace,and what cfms?

    FYI,the media filter would be best installed horizontially in the middle of the return drop,then vanes in the elbow going into the furnace,to lower the static.

    Just think the OP neded a better plan,to lower the static.

  15. #35
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    I think he is going to have the media filter installed horizontally.
    Atleast in another thread that came up.

    He has static issues in both his return and supply. And I think both need addressed. His supply static rises when he lowers his return static. Being that its a VS blower, doesn't that mean he's not moving set CFM.

  16. #36
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,835
    Post Likes
    Yes, I think he's moving less then it's set at.

    We have only seen that a statics higher then then have been mentioned,but I guess that depends on the model.

  17. #37
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Yorks drop off after .6". So if you have a .4" supply and .5" return, and then decrease the return, you see an increase in the supply.

  18. #38
    Join Date
    Apr 2008
    Location
    Princeton, NJ
    Posts
    627
    Post Likes
    Thread Starter
    I have re-measured and have decided to convert the 24x10 return drop to 24x18 or 24x20 (instead of 24x16 as previously planned). The bigger the better right?

    I do plan to have the filter installed horizontally in the Return Dop.

    I'm currently set at 350 CFM/ton which is theoretically 1400 CFMs for the 4 ton AC.

    The furnace is 100K btu in 95K but out.

    Key1

  19. #39
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,835
    Post Likes
    Quote Originally Posted by key1cc View Post
    I have re-measured and have decided to convert the 24x10 return drop to 24x18 or 24x20 (instead of 24x16 as previously planned). The bigger the better right?

    I do plan to have the filter installed horizontally in the Return Dop.

    I'm currently set at 350 CFM/ton which is theoretically 1400 CFMs for the 4 ton AC.

    The furnace is 100K btu in 95K but out.

    Key1
    Bigger isn't always better.

    If you increase the duct ,velocity(air speed) drops,if velocity increases again,like the reuduction in duct size to eneter the furnace,this increases the static.That said,this is often unavoidable,but when done just for amusement,it may do more harm then good.


    Looks in the pics like the return drop is tapped into a duct that is wider and shorter.If so ,removing he drop,and adding an elbow with vane to turn the return down,would be much less restrictive.

  20. #40
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    After you get so big. It has little effect.
    But won't hurt.

    Is he going to vane the return ell at the furnace. this will help a lot.

Page 2 of 3 FirstFirst 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •