Results 1 to 9 of 9
    hearth planet
    Ycas0150 Problems
    Hi The Chiller Displays High Current On Both Systems Fla% Is Over 115 On System 1 And Over 220% On Sistem 2
    Just Run For A Few Seconds And Shows High Current
    Feb 2007
    Northern NJ
    call an hvac company for service. no diy allowed
    Jun 2008
    Egypt
    hi
    in the first check:
    1- the water volum in condenser
    2- water temp. in condenser
    3- refrigerant level position in condenser (it's must be under 40%)
    4- check Actuator flow (orifice) work "it's between condenser and evaporator"
    if you found all that in normal work call company service.
    see you
    hearth planet
    Aamer This Is A 150 Tons Screw Air Cooled Chiller I've Changed The 3 Control Boards Incluiding Keypad And Eprom. Reprogram It All
    And Compressor On Sistem 2 Still Shows Too High %fla I Checked The Compressor And Looks Like It Starts Loaded To Me (slide Valve Stucked)
    I'm New Here And Besides That My English Is Not That Good So I Can Explain It All Clearly But I Will Never Give Up.
    Sometimes You Have To Play With Difficult Cards But That's What Keeps Me Alive. Thanks A Lot
    Aug 2000
    Under my tree
    Sounds like slide valves are stuck. JMHO
    To much work with too little time!!!!
    The Great country of Texas
    The micro may not be set up right for the current. I have found this problem before. You can measure the amps with a meter and scale the micro accordingly barring there is nothing wrong with the compressors
    "I'm from Texas, what country are you from?"
    Jan 2005
    NY
    Im having the same problem. I have seen many trane screws but this is my first york. It starts at 60 amps then loads to 140 amps with the unload solinoid unplugged so the slide valve must be moving I ordered a unload valve hoping this will fix it. I removed the old valve and it only moves about a
    1/16" I am thinking it should move more. If I am missing something please tell
    Philippines
    YCAS Chiller
    Hi
    My freind there is a separate password to access the settings of your chiller. Call the nearest York service office to fix your problem.
    Number 1 rule DO NOT REMOVE THE EPROM of YCAS chiller the program will reset to defaut.
    Confused
    Great, more secret handshake crap!