Results 1 to 10 of 10
Thread: Sizing issue
07-08-2008, 09:25 AM #1
- Jul 2005
- 27
Sizing issue
Greetings, I have some questions concerning sizing of two separate residential split systems in the same house. I have a job that is 2/3s complete and just needed some professional advice about sizing. Both systems R-22 3000 sq ft house two separate split systems, natural gas 90afue furnaces with straight cool, all brand new. It seems most of the hard work is done but owner had to pull contractor off for financial reasons. Now trying to sell house. Anyway first system has 3 ton blower , 4 ton indoor coil . Second system has 4 ton blower and 5 ton coil. Not sure what size condensing units to install or what the contractor had in mind when he oversized the indoor coils. Also wondering about piston size, do I size to indoor coil or outdoor unit? Thanks in advance.
07-08-2008, 09:28 AM #2
Very common to have lager coils then condensers.
Ask him for the other contractors load calcs. Or do your own.
07-08-2008, 10:05 AM #3
7 tons for 3000 sq ft?
07-08-2008, 10:13 AM #4
Maybe its all glass walls.
07-08-2008, 11:44 AM #5
- May 2008
- Lower Arkansas
- 27
The best way in my opinion is to size the condensers to the furnaces, 4 and 3 ton respectively. Size the pistons to the condenser size and enjoy the SEER boost of the larger evaporator coils. Personally, I would use TXV's instead of pistons to be assured maximum efficiency. Seven tons should do a real good job and save jingle on power bill - shorter cycles...Watch out for humidity if not variable speed furnaces with that high a BTU rating.
07-08-2008, 12:09 PM #6
Banned
- Aug 2002
- Office and warehouse in both Crystal River & New Port Richey ,FL
- 18,836
07-08-2008, 12:23 PM #7
- Jun 2007
- The Twilight Zone
- 2,964
07-08-2008, 01:27 PM #8AOP Forum Rules:
Rules for Posting
Rules For Equipment Owners
Equipment Owners Find a Contractor HERE!
udarrell
07-08-2008, 01:40 PM #9
Do a load calc, and quit guessing at size.
If the first contractor was planning wrong. Why do you want to follow in his footsteps.
07-08-2008, 05:08 PM #10
- Feb 2007
- 997