    compressor is pumping but not cooling

    Hello every one
    I am working on the 2 to unit made by carrier (HDR MODLE) which is i am getting 300 psi on high side and 60 psi on low side, the evap coil and condesor and filters are clean, when i touch the high side by compressor or evap coil is very hot but i don,t get any temp on low side is it posible the copressor is pumping but not cooling. thanks

  2. #2
    Join Date
    Jun 2004
    Location
    Howell, Michigan
    Posts
    16,158
    This is not a DIY help site. Please read the rules. My advice is to call a technician to properly diagnose your equipment.

    I also deleted your second thread on the same subject in General Discussion, once again, please review the rules re' posting etc.

  3. #3
    Join Date
    Oct 2007
    Location
    Aurora , Colorado
    Posts
    32
    hey i am a technician i been doing heating and cooling for 20 years but i never had a problem like this befor . thanks

  4. #4
    Join Date
    Mar 2008
    Location
    Kitchener, Ontario
    Posts
    508
    Quote Originally Posted by massoudv View Post
    hey i am a technician i been doing heating and cooling for 20 years but i never had a problem like this befor . thanks
    DIY

    what kind of compressor is it then? is it cap tube or txv what refrigerant is it on ?

  5. #5
    Join Date
    Jun 2004
    Location
    Howell, Michigan
    Posts
    16,158
    Quote Originally Posted by massoudv View Post
    hey i am a technician i been doing heating and cooling for 20 years but i never had a problem like this befor . thanks
    We can only answer technical questions in the pro forums. There is a link in my signature line, click and follow the directions.

  6. #6
    Join Date
    Oct 2007
    Location
    Aurora , Colorado
    Posts
    32
    is a 38hdr condensor with goodman coil and is a cap tube. thans

  7. #7
    Join Date
    Oct 2007
    Location
    Aurora , Colorado
    Posts
    32
    and is R22 refrigerant .

  8. #8
    Join Date
    Apr 2004
    Location
    Charlotte, NC
    Posts
    648
    Quote Originally Posted by massoudv View Post
    Hello every one
    I am working on the 2 to unit made by carrier (HDR MODLE) which is i am getting 300 psi on high side and 60 psi on low side, the evap coil and condesor and filters are clean, when i touch the high side by compressor or evap coil is very hot but i don,t get any temp on low side is it posible the copressor is pumping but not cooling. thanks
    If you are not DIY, what does "high side by compressor or evap coil is very hot" mean, exactly? What refrigerant is in this unit? The real question is 'why is there such a difference between high and low side pressures?' 300 and 60 are not r22 typical pressures for an 85 degree day and high space temperature. Seems like a restriction, and you should have seen this within the 20 or so years of a/c work. Good luck.
    "Fighting Ignorance since 1973 (It’s taking longer than we thought)." The Straight Dope.

  9. #9
    Join Date
    Jun 2004
    Location
    Howell, Michigan
    Posts
    16,158
    I am not trying to give you a difficult time. But our rules are here for a reason. Please review them, no technical help in this forum guys! PERIOD!

  10. #10
    Join Date
    Mar 2008
    Location
    Kitchener, Ontario
    Posts
    508
    DIY

  11. #11
    Join Date
    Jun 2004
    Location
    Howell, Michigan
    Posts
    16,158
    Quote Originally Posted by bdivell View Post
    DIY
    Good move on the edit!

  12. #12
    Join Date
    Oct 2007
    Location
    Aurora , Colorado
    Posts
    32
    it was 72 at the evap and when i check the superheat was 22 deg but sinse i was not getting the right temp i did not check the subcooling.

  13. #13
    Join Date
    Mar 2008
    Location
    Kitchener, Ontario
    Posts
    508
    HeyBob i wasn't trying to help him at all

Page 1 of 3 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event