    What type of Thermometers do you guys use when doing superheat calc.

    You know when you are taking the temp of the suction line and indoor/outdoor dry bulb temp. Are non-contact therm ok? I was looking at these.

    http://www.harborfreight.com/cpi/cta...emnumber=93984

    http://www.harborfreight.com/cpi/cta...emnumber=95382

    The probe thermometer seems appropriate. But i've mainly seen people use the thermometers that have the wire that you can put anywhere. Like wrap it around the pipe and so on.

  2. #2
    Join Date
    Jul 2001
    Location
    VA
    Posts
    2,801
    Post Likes
    I wouldn't use either of those.

    Look at the testo contact thermometer, many use the thermocouple temp probe with a meter, there are pipe clamp options for many meters, and there are standalone temp devices.

    but the two you picked are inadequate for any serious work.
    ___________________________________________


  3. #3
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,847
    Post Likes
    Pipe clamp thermocouples are the way to go. You clamp it on and plug it into a multimeter that can read it, or a device like my Fieldpiece superheat/subcooling meter-calculator, which also reads system pressure. If your tool budget is fat you can get a digital gauge manifold that has everything on board. You merely connect the manifold as a standard analog gauge manifold, hook up the pipe clamp thermocouples, and you're good to go.

    High quality instruments + high quality analysis = high quality diagnosis = high satisfied customer/low callback ratio. Gotta love that kind of math.

  4. #4
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Cooper SH66 for DB readings.

  5. #5
    Join Date
    Jun 2008
    Location
    South,Tx
    Posts
    341
    Post Likes

    Field Piece

    Field Piece with "K" type ,Model # SC 67
    Buy the one in the blue bag , comes with the clamp to read Temp
    Last edited by derbysr; 07-07-2008 at 10:25 AM. Reason: spelling
    Matt 7:12 The Golden Rule
    "Do for others what you would like them to do for you. This summary of all is taught in the law and the prophets.

  6. #6
    Join Date
    Jun 2008
    Location
    Las Vegas, NV
    Posts
    224
    Post Likes
    Fieldpiece ST4.

    Barrie

  7. #7
    Join Date
    Jun 2005
    Location
    SW Wisconsin
    Posts
    6,627
    Post Likes
    DPSwitch, beenthere & shophound, or anyone, - I had & used both, a refrigeration clamp-on dial read & a digital strap-on pipe surface probe for SH & SC, I used both at the same time to get SH & SC.

    At some of the HVAC Supplies near me in NE Iowa, ONE (Heil supply) had NO thermometers of any kind, NO anemometers to check velocities, & NO inclined manometers, NO magnehelic gages with which to check ESP, etc., you coulsd NOT buy anything there!

    No wonder I see none of them with all these necessary instruments, nor doing these critical checks toward good A/C performance! What is happening to HVAC here in the Midwest North country? - Darrell

  8. #8
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Some supply houses don't want to stock tools that don't have high sells volume.
    Those are often the same places that don't put on any training classes either.

  9. #9
    Join Date
    Jul 2006
    Location
    NW burbs of Detroit
    Posts
    6,058
    Post Likes
    Quote Originally Posted by DPSwitch View Post
    I wouldn't use either of those.

    Look at the testo contact thermometer, many use the thermocouple temp probe with a meter, there are pipe clamp options for many meters, and there are standalone temp devices.

    but the two you picked are inadequate for any serious work.
    Dip is right. For one thing the Harbor Fright is junk. The IR tester is not good cause you can get false readinf.

    The stem thermometer cannot be attched to the SL to get a good reading.

    I have a four station CPS Temp Seeker. I have an an alagator type probe for SC and a disck shaped probe with a convex surface to read SH.

    It also has a dry bulb and RH probe. Under Two Bills,

    Google CPS Temp seeker. It's moderately priced and is accurat. If you got money to burn buy Testo, Tif Fluke and a slew of others with multi port capability

  10. #10
    Join Date
    Jul 2001
    Location
    VA
    Posts
    2,801
    Post Likes
    The temp seeker lets you monitor 4 temps at once which is a plus.
    ___________________________________________


Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •